lol yes i am bud
http://s1288.photobucket.com/user/David_Reason/media/CU/20140714_182428_zps840d5abf.jpg.html?sort=3&o=0
http://s1288.photobucket.com/user/David_Reason/media/CU/20140714_182405_zps52b68014.jpg.html?sort=3&o=1
30ma
so i don't need to add a new earth then just make sure one earth is in one terminal and the earth is in the other terminal and same at the board one in one terminal and the second in a different terminal ? and yes i can do elec work i just like to make sure its right before i start the work then...
ok by high integrity you mean a second earth from the CU to the Socket(s) that are being used by the server rack then back to the CU Using 4.5mm earth?
Am i able to carry out this work my Self
its going to be a small setup 4-6 servers and 24 port switch and a patch panel im being told by some people to earth it and some saying theres no need on such a small setup
existing equipment? and its going to be housing servers and network switches and a pdu and it will be about 60-100 feet away
my boiler is in the same room as the rack is going to be and i no the gas pipes are boned could i just boned to that or is that a no no ?
ok what size earthing cable should i use? and will it be ok to run out side as that is the simplest way to get back to the meter as i don't want to be pulling up floor boreds
ok what size earthing cable should i use? and will it be ok to run out side as that is the simplest way to get back to the meter as i don't want to be pulling up floor boreds
The pdu says it must be earthed could i earth it to a radiator pipe? or my friend said to put a earth wire on and then put it in a earth pin on a plug and plug into a plug socket on the same ring as the servers and so on is this ok to do or is my way better ?