Recent content by intamixx

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. I

    Phase Neutral Reverse Fault on Kitchen socket

    Hello, Thanks for the replies. I triple checked that the single socket was wired correctly.  Live(brown), neutral(blue), earth (yellow/green).  It looked good to me but no I don't have any pictures of it, will try to get some. I have tried the tester socket on an alternate good socket which...
  2. I

    Phase Neutral Reverse Fault on Kitchen socket

    I have a strange problem with some sockets in my kitchen and was wondering whether anyone can shed some light on this problem. I have a "master" twin socket that has a "slave" single socket.  Both sockets are in the kitchen and on the inside wall of which the exterior side faces the garden. ...
  3. I

    Consumer unit not 17th edition edition

    Found a view of the front of the house showing the gas bonding going under the floor boards.  Not sure how they missed this.
  4. I

    Consumer unit not 17th edition edition

    I've been to the property and had a look at the gas and water bonding.  I lifted up a few floor boards in the kitchen and under stairs cupboards and found the gas and water earth bonding.  The gas bonding runs under the floorboards to the outside gas meter and the inlet water pipe is bonded. ...
  5. I

    Consumer unit not 17th edition edition

    I will try and post the masked full report later on with a better picture of the consumer unit when I go there later today to put in the gas / water earth bonding. There is also an earth rod on the outside of the wall behind the consumer unit.  See picture, what is it? and what is it there...
  6. I

    Consumer unit not 17th edition edition

    The electrician was Part P and in there for an hour.  I have paid 95 plus VAT.  The house is a 3 bedroom end of terrace. I found the electrician online via his professional looking website as he was local to the area. There is no outside socket. See attached image of report listing issues and...
  7. I

    Consumer unit not 17th edition edition

    Hello, I have just had an Eicr done as I'm letting out the house. The electrician has stated the following points as c2. My consumer unit apparently is an old Wylex one. - consumer unit not 17th edition. - consumer unit main switch is 100ma - cooker switches wall socket outlet only on 100ma...
  8. I

    Cooker Switch close to Taps

    The socket is on a solid wall and the outlet to connect the electric cooker sits directly below the socket a few centimeters above the floor. The EICR report is required as the property will be let out.  The estate agents have requested this.
  9. I

    Cooker Switch close to Taps

    I've just purchased a property and require an EICR report. The previous owners fitted the kitchen themselves by the look of it and the estate agents have mentioned that the cooker switch is too close to the kitchen taps. Please see attached picture. Both switches are required to come down in...
Top