Thisis where the confusion started. I was glanding off into the consumer unit. The electrician who I subbed the job off say tails must be double insulated. Hence my comment have I missed something that changed in the 18th edition.
Thanks for the reply. I am doing this for another electrician. He started qioting from the regs about double insulated tail. What I tried point out this was for TT system.
He was saying I had to use an adaptable box etc. He had me doubting myself tbh I thought I had missed something in the 18th.
I have a swa supply from the house to the annex about 3 meters from the house.
The question is can I terminate the swa into the annex comsumer unit?
I know in a TT system the tails need to be double insulated. Can I terminate single insulated from the SWA on a TNS system?
All be it some time ago . I have come across this a few times with Pyro ( micc )
IR testing at 500v then 1000v actually dried it out and gave me perfect reading's
Without using a piece of string, :innocent
only really mark lighting cable before 2nd fix.
knick / sw drops / cross cut L in L out / and a crease with pliers for any loops .
No marks are left when I am finished.