    3 phase supplies

    no nothing other than what ive said no good really
  2. P

    3 phase supplies

    the amperage for the mccb is coming out at 160a 3 phase but sounds too low to me ?
  3. P

    3 phase supplies

    I would imagine that would be full start up power probs run at alot less
  4. P

    3 phase supplies

    That's the total load for the machine and is 3 phase neutral when I put it into my cable calc this is what its bring out 70mm 4 core swa 90degree ?
  5. P

    3 phase supplies

    from a main panel 1600A
  6. P

    3 phase supplies

    around a 70mm 4 core swa is what im getting
  7. P

    3 phase supplies

    yes the incoming supply can take it. This is the information that was emailed to them from the manufacturers and require a supply for each one.
  8. P

    3 phase supplies

    Hi all, I Have been asked to put some 3 phase supplies in a factory 4 panels each rated at 120kw, 117kw 123kw and 115kw the length of the run is about 70m for each one and was after a bit advice of what size cable and mccb to use for each one will be on tray plate at high level. Any advise would...