Forums
New posts
Search forums
What's new
New posts
New media
New media comments
Latest activity
Media
New media
New comments
Search media
Members
Current visitors
Log in
Register
What's new
Search
Search
Search titles only
By:
New posts
Search forums
Menu
Log in
Register
Install the app
Install
General Forums
General Chat Area
Duel Source Towel Rail Problems
JavaScript is disabled. For a better experience, please enable JavaScript in your browser before proceeding.
You are using an out of date browser. It may not display this or other websites correctly.
You should upgrade or use an
alternative browser
.
Reply to thread
Help Support Talk Electrician Forum:
This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Message
<blockquote data-quote="mvkpe1" data-source="post: 371993" data-attributes="member: 14992"><p>I agree that the test between L&amp;N was probably the resistance of the element I was more concerned with the L-PE and N -PE both reading 0.0M ohms, which would of course trip the RCD.</p><p></p><p>I would also agree that maybe the original element wasn't faulty, hence why the question about any ideas where or what to start looking for. The circuit in question works perfectly without the element connected.</p></blockquote><p></p>
[QUOTE="mvkpe1, post: 371993, member: 14992"] I agree that the test between L&N was probably the resistance of the element I was more concerned with the L-PE and N -PE both reading 0.0M ohms, which would of course trip the RCD. I would also agree that maybe the original element wasn't faulty, hence why the question about any ideas where or what to start looking for. The circuit in question works perfectly without the element connected. [/QUOTE]
Insert quotes…
Verification
Post reply
General Forums
General Chat Area
Duel Source Towel Rail Problems
Top