Forums
New posts
Search forums
What's new
New posts
New media
New media comments
Latest activity
Media
New media
New comments
Search media
Members
Current visitors
Log in
Register
What's new
Search
Search
Search titles only
By:
New posts
Search forums
Menu
Log in
Register
Install the app
Install
General Forums
General Chat Area
Unusual earth fault
JavaScript is disabled. For a better experience, please enable JavaScript in your browser before proceeding.
You are using an out of date browser. It may not display this or other websites correctly.
You should upgrade or use an
alternative browser
.
Reply to thread
Help Support Talk Electrician Forum:
This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Message
<blockquote data-quote="kerching" data-source="post: 531704" data-attributes="member: 11861"><p>So,L-N 230</p><p>L-CPC NOT 230.....so,what was it ? 229; 200,3???</p><p>Insulation test results?</p><p>Loop,test results</p><p></p><p>Nowhere near enough info, and a multimeter is not really a suitable tester </p><p></p><p>What was the original fault reported? Dodgy/broken socket?</p></blockquote><p></p>
[QUOTE="kerching, post: 531704, member: 11861"] So,L-N 230 L-CPC NOT 230.....so,what was it ? 229; 200,3??? Insulation test results? Loop,test results Nowhere near enough info, and a multimeter is not really a suitable tester What was the original fault reported? Dodgy/broken socket? [/QUOTE]
Insert quotes…
Verification
Post reply
General Forums
General Chat Area
Unusual earth fault
Top