Installing On A Tt System

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

redman

Member
Joined
Mar 7, 2009
Messages
85
Reaction score
0
Location
Nottingham
Hi,

Could someone please confirm that I am thinking along the right lines with this. (Ive never worked on a TT system)

Just as an example........Say I install a circuit on a TT system.

The Ze reading is 16 ohms 

The R1 + R2 reading is 0.25 ohms.

So if i calculated the Zs, it would be 16.25 ohms.

Obviously this is going to be alot higher than the max Zs values in the BGB,

But because every TT circuit should be RCD protected, my disconnection time would be less than 0.2 seconds.

So.....would this be the way to conform to the current regs ?

Cheers

 
Just before the discussion starts about your reads,

are your RCD devices double or single pole?

 
Ok heres one for you. 

An eicr (a few actually)  gets a Unsatisfactory because the RCBO's used on all socket circuits are above the 80% & knocking on for being on the 100% value for Zs for the over current / mcb portion of the device (they would they are type C), yet the same company that did some of this work (fitting RCBO's) 2 years ago filled out the eic as 1667 for Zs  :C

 