110V Cte Transformer


Sidewinder

Question

Sidewinder

Looking at a job in a factory during the summer shut down.

 

Part of it is to fit a permanent 400:110V CTE transformer say around 5 - 10 kVA and then run out to 60309 sockets around the factory.

Full details are being worked on.

Just wondering who would you go to for the transformer?

 

I have tried a few already and am awaiting replies, but I am looking more for recommendations of quality/service/support, IYKWIM.

 

Even if I work the spec with the manufacturer and then purchase through a wholesaler.

I don't want to be going through a 3rd party to sort the spec really.

 

Then I have to overcome getting MCCB's for the old MEM panel board, they are a type which seem to be obsolete!

Client will go bonkers if they have to consider changing the panel board, so will I.

I don't think that they will consider used, but I may be putting that to them and wording the contract such that we won't warranty the kit.

 

Link to comment
Share on other sites
 

16 answers to this question

Recommended Posts

Hi Sidewinder

 

"Then I have to overcome getting MCCB's for the old MEM panel board, they are a type which seem to be obsolete!"

 

I'm in the middle of a job that needed MCCBs for a MEM2 board. I have it direct from Eaton technical that they are about 12 years obsolete so your only chance is ethingy, which personally I wouldn't chance. Solved my problem with an additional Proteus MCCB board, not my first choice but money is an issue.

 

Regards

Martin

Link to comment
Share on other sites
 
Sidewinder

Thank you Martin, I was pretty convinced that they were obsolete, poor show from Eaton TBH, Schneider will still supply compatible stuff for most of their old boards.

Typical Yanks, it's our way or the Highway.

 

I have done the add on panel board thing before, but that was to a 1600A unit with fuse switches.

The annoying thing about this panel board is it is an 8 way (ish) could be more with most of them free.

 

Problem has been overcome anyway in the meantime, there is a Schneider (MG) Type B board the other end of the line, so we will use that, the loads are only small, we were just looking to offer the client another power centre.

Link to comment
Share on other sites
 
kerching

Thank you Martin, I was pretty convinced that they were obsolete, poor show from Eaton TBH, Schneider will still supply compatible stuff for most of their old boards.

Typical Yanks, it's our way or the Highway.

 

I have done the add on panel board thing before, but that was to a 1600A unit with fuse switches.

The annoying thing about this panel board is it is an 8 way (ish) could be more with most of them free.

 

Problem has been overcome anyway in the meantime, there is a Schneider (MG) Type B board the other end of the line, so we will use that, the loads are only small, we were just looking to offer the client another power centre.

Don't forget my PM....if suitable they can be put on hold

Link to comment
Share on other sites
 
ProDave

There's a technical issue here.

 

110V CTE means it's a single phase transformer, so even if it's a 400V primary it's still only single phase.  but I'm sure you knew that already.

 

I only mention it as you can buy 3 phase 400V to 110V transformers but they won't be CTE.

 

If you want to load balance therefore, three smaller 400V to 110V  CTE transformers would be the way to go.

Link to comment
Share on other sites
 
Andy™

ive used http://www.ete.co.uk/ a few times



I only mention it as you can buy 3 phase 400V to 110V transformers but they won't be CTE.

 

erm... they are CTE... simply 3 phases with 110v P-P, or 63v P-E

Link to comment
Share on other sites
 
steptoe

I fitted some about 4or5  years ago, will try and dig out what they were. 

Link to comment
Share on other sites
 
ProDave

ive used http://www.ete.co.uk/ a few times

 

erm... they are CTE... simply 3 phases with 110v P-P, or 63v P-E

Yes I can see that now, but a "proper" 110V CTE tx is 55V p-e. you can't achieve that with a 3 phase tx.

 

If the customer will accept a 3 phase star wound secondary tx 110V p-p, with the star point earthed, then go for it, but to my mind that's not quite a proper CTE.

 

The distribution board from the tx to the sockets could be "interesting"

Link to comment
Share on other sites
 
Andy™

if its star with centre point connected to earth, then its CTE...

 

 

for the DB, s normal TP board using DP MCB's would work

Link to comment
Share on other sites
 
Sidewinder

Sorry, yes my poor description perhaps.

The supply is 2 x 230V input, thus 400 V between two phases, which is kind of single phase, but I don't like the term, to me it's two phase, it can't be 3 phase, which I why I didn't say 3 phase.

I am looking at 2 x 55V CTE output, it's for "yellow" plugs IYKWIM.

They want to do away with carrying transformers around and have fixed 110 distribution down the lines for maintenance works.


DB between Tx & sockets will be full of DP breakers not unusual, mind I might, get the "DB" built into the transformer housing.

Link to comment
Share on other sites
 
ProDave

So it's a single phase 400V in 55-0-55 out

Link to comment
Share on other sites
 
Andy™

many have built in MCB's, could you not connect your additional sockets to these instead of a separate DB?

Link to comment
Share on other sites
 
Apache

60309 sockets around the factory.

That's a hell of a lot of sockets Sidey..............

 

:D

Link to comment
Share on other sites
 
Sidewinder

Ha ha!

Link to comment
Share on other sites
 
septiclecky

 60309 sockets around the factory.

 

 

 

That's a hell of a lot of sockets Sidey..............

 

:D

 

 

Be a bloody big transformer he would need as well

Link to comment
Share on other sites
 
Sidewinder

Dai Versity is a very good friend mind Septic! ;)...

Link to comment
Share on other sites
 
septiclecky

Dai Versity is a very good friend mind Septic! ;)...

 

 

Whats a dance group got to do with it?

Link to comment
Share on other sites
 

Archived

This topic is now archived and is closed to further replies.

×
  • Create New...

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.