Asked to check the wiring at the local clay pigeon club.
Clubhouse was fine, but then I inspected the traps. First 3 were fine, fed with SWA (presumed buried at correct depth) and tested ok.
Trap 4 fed with YY that came up through a large white pipe (source not yet found) and found not to have any earth, and nothing in that trap earthed. And from here, a bit of 1.5mm flex disappears into the ground (containment if any not visible) and appears in trap 5 some 50 metres away.
They can't understand the problem. "it works"
Clubhouse was fine, but then I inspected the traps. First 3 were fine, fed with SWA (presumed buried at correct depth) and tested ok.
Trap 4 fed with YY that came up through a large white pipe (source not yet found) and found not to have any earth, and nothing in that trap earthed. And from here, a bit of 1.5mm flex disappears into the ground (containment if any not visible) and appears in trap 5 some 50 metres away.
They can't understand the problem. "it works"