You are told it is a 16A circuit, you are not given the design current, if you specify a type B 16A BSEN60898 then maximum Zs @70°C is 2.73Ω

Ze is 0.11Ω, therefore R1+R2 must be less than 2.62Ω @70°C.

From the installation method (singles in conduit) and assuming maximum current as you do not have the design current, the cable minimum cable csa is 2.5mm².

If you choose 2.5mm² for the cpc size the resistance R1+R2 is much lower than 2.62Ω so Zs will be compliant.

and then calculate using the rearranged adiabatic equation from 434.5.2

t = k²S²/I² = 115²*2.5²/2090² = 0.019s  if the circuit breaker will disconnect in that time then the cpc is OK.

You can also check at the end of the circuit to find 0.3s which is also OK.

Share this post


Link to post
Share on other sites
Pops1
1 hour ago, Ardet R said:

You are told it is a 16A circuit, you are not given the design current, if you specify a type B 16A BSEN60898 then maximum Zs @70°C is 2.73Ω

Ze is 0.11Ω, therefore R1+R2 must be less than 2.62Ω @70°C.

From the installation method (singles in conduit) and assuming maximum current as you do not have the design current, the cable minimum cable csa is 2.5mm².

If you choose 2.5mm² for the cpc size the resistance R1+R2 is much lower than 2.62Ω so Zs will be compliant.

and then calculate using the rearranged adiabatic equation from 434.5.2

t = k²S²/I² = 115²*2.5²/2090² = 0.019s  if the circuit breaker will disconnect in that time then the cpc is OK.

You can also check at the end of the circuit to find 0.3s which is also OK.

 

Thank you, that's helped. Would you say the Design Current to be 16A, then your In could be 20A? I will have another go at the calculation, just so I understand how you have done it. Thanks once again. 

Share this post


Link to post
Share on other sites
poni

can you use the conduit as the cpc?

 

Share this post


Link to post
Share on other sites
Pops1

So I had a go:

 

Circuit 16A

Ib 16A

In 16A

Zs for a 16A Type B is 2.73Ω

Ze is 0.11Ω

Zs - Ze = R1+R2 = 2.62Ω

Table I1 CSA 2.5mm²

In 21.27A

Cable Size: 2.5mm² Ref Method B Volt Drop: 18

Actual Volt Drop: 8.64v

Maximum VD: 11.5v

Calculate Actual R1+R2 = 7.41x30x1.20 / 1000 = 0.26676Ω + 0.11Ω = 0.37676Ω

UoxCmin / Zs = 80A looking in BS7671 16A Current is 80A

Adiabatic equation.
 

230/0.11 = 2090A

I then modified to get an exact time: t = k²S²/I² = 115²*2.5²/2090² = 0.019s

2090² x 0.019 = 82993.9

Square Root of 82993.9 = 288.0866189/115 = 2.505mm²

Cable Size 2.5mm²

Share this post


Link to post
Share on other sites
Ardet R

From table 54.7 a 2.5mm² conductor is OK, so however you calculate the adiabatic equation it should come out as suitable.

You can't put 2.5mm² into an equation, square it multiply it and divide it and then reverse the process to get the same answer you put into the equation as it is meaningless. e.g. 2.5 *3 /10 = 0.75...  0.75 *10 / 3 = 2.5

As this is a project you should need to do some research for it and perhaps get I²t values for your breakers.

In essence the adiabatic equation is fairly pointless without these values unless you are checking very low fault currents.

Share this post


Link to post
Share on other sites
Pops1
5 hours ago, Ardet R said:

From table 54.7 a 2.5mm² conductor is OK, so however you calculate the adiabatic equation it should come out as suitable.

You can't put 2.5mm² into an equation, square it multiply it and divide it and then reverse the process to get the same answer you put into the equation as it is meaningless. e.g. 2.5 *3 /10 = 0.75...  0.75 *10 / 3 = 2.5

As this is a project you should need to do some research for it and perhaps get I²t values for your breakers.

In essence the adiabatic equation is fairly pointless without these values unless you are checking very low fault currents.

 

Okay thanks. We have not been told to do any research on breakers, and we have not given any manufacturers data, in the specification. The question does not ask for it either. I have asked for some more help. They have come back with:

 

So I have asked them for some guidance:
 

  • Calc CPC size using selected Circuit Breakers Zs.
  • Then work out R1+R2
  • Select cable from Table I1 to meet minimum R1+R2 value.
  • Once the cable is selected, work out actual R1+R2 and calculate actual circuit Zs - including correction factors 1.20
  • Calc to confirm actual CPC size using Adiabatic Equation.
  • Circuit length needs to be greater than 15m.

Share this post


Link to post
Share on other sites
Ardet R

So you have done all that except the fifth one to resolve the adiabatic equation for confirming the cpc size.

 

I also missed your post of "Thank you, that's helped. Would you say the Design Current to be 16A, then your In could be 20A? I will have another go at the calculation, just so I understand how you have done it. Thanks once again."

The question states the circuit is 16A this would mean a circuit with a 16A circuit protective device.  in the Hint section it also states  "the max (R1+R2) for the circuit based on the Zs for a 16A protective device" Therefore your In must be 16A and based on that your Ib is less than or equal to 16A (in all likelihood your Ib for two fridges is going to be less than 7A based on commercial fridge specifications).

 

If you calculate your modified adiabatic equation using the fault current at the end of the circuit using I = V/R =V/Zs = 230/0.3767=611A and with S as 2.5 and k as 115 then you get 0.22s which is larger than the maximum possible trip time of 0.1s and so is compliant.

This does not address faults earlier in the circuit, however.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.