1st off Happy New year all not been on for a bit.
My question is I've done a CU upgrade and also fitted a new earth rod as readings were about 400ohms got it down to 20ohms by driving it into the existing rod hole once removed, think it may be touching the old lead water pipe now.
Sorry I'll get to the point the gas is bonded in 6mm and cutomer will not pay for 10mm upgrade as its a half day of work lifting boards etc. so here is the question if table 54.1 in the 17th states that the main earth conductor can be as litlle as 2.5mm if protected against mechanical damage & corrosion then is it ok to leave the 6mm? and if you think the regs require it to be 10mm can it be listed as a Code 2 on the install cert?
My question is I've done a CU upgrade and also fitted a new earth rod as readings were about 400ohms got it down to 20ohms by driving it into the existing rod hole once removed, think it may be touching the old lead water pipe now.
Sorry I'll get to the point the gas is bonded in 6mm and cutomer will not pay for 10mm upgrade as its a half day of work lifting boards etc. so here is the question if table 54.1 in the 17th states that the main earth conductor can be as litlle as 2.5mm if protected against mechanical damage & corrosion then is it ok to leave the 6mm? and if you think the regs require it to be 10mm can it be listed as a Code 2 on the install cert?