I stand corrected by sir Slips of the Shod lands...Sorry Special location, some of that is wrong. An isolator is a switch & has no overload protection (ie, fuse).If the distribution board is any distance away from the supply origin (normally more than 3 m) then a switch fuse has to be fitted.
Most new installs now have an isolator, which is fitted soley so you can work on the consumer unit safely without having to break a DNO seal and remove the main fuse (which is not allowed anyhow)
Indeed!If every installation had them we'd never have the cutting of seals issues
First of all sorry to drag this thread back up.Sorry Special location, some of that is wrong. An isolator is a switch & has no overload protection (ie, fuse).If the distribution board is any distance away from the supply origin (normally more than 3 m) then a switch fuse has to be fitted.
Most new installs now have an isolator, which is fitted soley so you can work on the consumer unit safely without having to break a DNO seal and remove the main fuse (which is not allowed anyhow)
Thanks. I'm into a bottle of red myself now but can see your point. I'm going to incorporate a switched fuse to cover the eventualities.safedepth, as with all regulation some will and do interperate differently. If you look through the regulations about isolation there are clear indications as to why isolation is provided and when it should be used. Again we often have a bleed over of regulations some taking precedent over the others.I have had a few drinks tonight and I am not of clear thought, so what I say is from memory only, I do know that any length over 3m should be isolated at or near the in comming supply, if this is a building regulation or a DNO imposed regulation I can not remember, but from a BS7671 point of veiw I can see a requirement under isolation for any single point of use ( consumer unit) , in this case, will require safe isolation, some DNO's now fix this as standard, some do not.
As with all regulation, the best aproach to any works is to follow the best practice guides, its the no nonsense, does what it says on the tin, approach to all electrical installations.
Cheers sparky. It wasn't so much the isolator but the fuse I was querying. For what it's worth I think a switch should always be incorporated between the DNO fuse and cu. These cu's will be 15 m from the head.The isolator between the Meter and Consumer Unit came into use on New housing developments to enable connection of the Supply and fitting of the Meter to be completed PRIOR to completion of the internal installation. Contractors were then allowed to "self connect" safely to the outgoing terminals of the 100 Amp double pole isolation switch and a PME earth connection point pre fitted.
It would be a bit difficult where you have Eco 7 heating installations and the like. It is quite acceptable to have multiple Main switches in the same location.Would an isolator also be fitted if there is more than one CU, so that there is one point of isolation for the whole house?
In that instance you'd just use a TP&N isolator.... not a problem at allIt would be a bit difficult where you have Eco 7 heating installations and the like. It is quite acceptable to have multiple Main switches in the same location.