Joint On A 3-Phase Sub-Main

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

unphased

Senior Member
Joined
Feb 13, 2008
Messages
192
Reaction score
19
Location
Tamworth
WP_000098 resized.jpgThought this might interest you guys. Supply is to a 4-way 3-phase board fitted with a 63A 30mA triple pole switch on a TT earth. Located in a unit rented out to various companies who want it. Cable is 4-core 10mm2 SWA and the joint is an IP65 adaptable box, 30A jb and a connector for the neutral.

 
Hi Marvo. Yep definitely 10mm2. Camera has distorted appearance. Screwfix forum think its fine. Nowt wrong with it. 30A rated accessories on a sub-main though. :huh:

 
Agree, no way would two 10mm's fit a 30A junction box.

Whether it's "okay" or not depends on the OCPD feeding it. >30A then no it's not okay.

 
Well it looks like 6mm to me, sorry.

If you look at the size of the earth bolt [nice use of the banjo/plasic box/nut technique] it appears the same size of the cable if not bigger. AND it looks like a galv 6mm gutter bolt [nice]... You have to zoom in a lot,

Looks like too much slack in the terminals to have 2 x 10mm in them..............just saying

 
Last edited by a moderator:
Got to agree with the others ^

Looks like 6.0mm SWA to me,, the earth looks to be 10mm and the live conductors look to be smaller than it (from here that is!)

Also, although looking unconventional, the JB might be ok dependant on the sub mains OCPD

 
Last edited by a moderator:
If that`s a 10mm cable then Albert`s my Grandad!

( IIRC, that makes paddler a relative, too :slap )

As others have said, depends on the OCPD - but I wouldn`t like it personally!

 
Right then. I have been to site today and have all the info now. It IS 6mm2 (my humble apologies ;  ). The source is a distribution board inan adajacent shed around 30m away. Its on a 63A triple pole mcb. Main switch on the board is a 100A 100mA RCD. I haven't altered the joint just labelled it 400V. Its a mash up really. Also its daft why it was ever jointed. The joined length is around 3m and it would have made more sense to have put the fuseboard in a different position to avoid a joint. So its a 63A supply on a 6mm2 4-core SWA serving a 4-way 3-ph board.

:C

 
Last edited by a moderator:
So it fails on an inadequate rated junction box, inadequate rated cable, and in all probability (depending on length) excessive volt drop.

The only solution is rewire with thicker cable (and avoid the junction)

Or, if the load current is low enough, reduce the OCPD of the source.

 
I agree, too, but it ain't gonna be rewired, thats for sure. I could recommend a swap out of OCPD for a 50A but decision to do it is out of hands. Farmer owns the place. Joke is the biggest circuit on the fuseboard is mine, a 38m long 3-core 16mm2 SWA hooking up a portacabin. At least VD on that wont be an issue. ;)

 