Recent content by SparkyQuestions

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. S

    Eicr copper showing as it enters pendant comnection

    Just bad termination no stress or anything. I just wandered what people thought on the matter seemed to cause abit of a rucus between the testing lads where i work
  2. S

    Eicr copper showing as it enters pendant comnection

    Mentor/tutor i made my opinion but it started abit of a hussle and bussle at work and i was just interested on what people thought. If you read the original question i didnt say what is the answer to this i simply asked for opinions. As im always interested in what people think espically when it...
  3. S

    Eicr copper showing as it enters pendant comnection

    Where did you get this from have you ever heard of a magical thing called a dead test very cool. I was performing the cool trick of a R1R2 and while i do this i do a visual inspection 😱😱😱. I was simply saying if for say copper was showing in a light terminal and someone was to remove it he...
  4. S

    Eicr copper showing as it enters pendant comnection

    Ive asked a question about me questioning why some sparkys are saying c2 and some c3. I simply wanted to know what other peoples opinion was on the matter. And from your responses id guess you dont know the answer so you ve chose to tell world your a tutor who is to busy complaining about people...
  5. S

    Eicr copper showing as it enters pendant comnection

    As i said the landlord we work for is a nightmare dont know if he goes through insurance or somthing but years of working for him he would rather us tell him faults simple as a sticker not being present then us fix it on the spot. A very strange man
  6. S

    Eicr copper showing as it enters pendant comnection

    1. Just a question no one knows everything. 2. Not that i dont know just i like getting 2nd opinions on matters when multiple different sparkies have different opinions on one matter. 3. Its just a question if no one ever questioned anything no one would learn. 4.your so clever just answer it...
  7. S

    Eicr copper showing as it enters pendant comnection

    From what ive always been taught any copper showing was a big no no and my previous companys have always stated as a c2 giveing the reason that if someone was to take it off and had a fiddle theres a high chance of getting zapped but you could say that about anything. Just where ive moved...
  8. S

    Eicr copper showing as it enters pendant comnection

    I would yes for your average customer but this perticular one doesnt work like that he d rather we come back out of my control
  9. S

    Eicr copper showing as it enters pendant comnection

    If you take the pendant/bayonet cover off yes but in terms of when its closed up no
  10. S

    Eicr copper showing as it enters pendant comnection

    I can see your quick to throw a dig but not quick enough to read or answer the question. Did you see the bit where i said the landlord who we ve worked with many of times said do not fix any problems you find and thats means anything simple as it may be. But im not in the buiness of ignoreing...
  11. S

    Eicr copper showing as it enters pendant comnection

    Just completed a eicr i found connections in a light fitting had not been terminated correctly and had copper visable from outside the terminal. Far as i was away and taught that would be a c2 but im being told that its a c3 by other electrcians. Wandering what everyones opinion on this is i...
  12. S

    Led randomly dimmed

    Trust me when i say we ve tested everything voltage is steady no fluctuateing at all everythings fine tried a couple brands of downlights and it seems to have solved itself. If it was the voltage id expect it to effect other downlights 10 on the sams circuit no problem at all. Put it down to...
  13. S

    Led randomly dimmed

    Fittings been changed and the bulbs multiple times nothing seems to be wrong at all leaning towards just some bad luck
  14. S

    Led randomly dimmed

    Leaning more towards bad luck lamps are standerd bulbs never had a problem all the othet lights on the floor are the same becoming a mystery
  15. S

    Led randomly dimmed

    Checked all the connections all in wagos tight and fine its in the middle of a run and all the other ones are fine. Have tested the surrounding downlights as well to double check it all but no visable fault that we can find
Top