Quote:
Originally Posted by mercurystar999 View Post
The regs tell me anything plugged in is not part of the fixed wiring.
Where?
I would agree with that, BS7671 is only applicable to the fixed wiring up to any sockets, lighting points and associated switches etc..
What the client connects...
On a personal note, a fuse in the Neutral has to be a very dangerous scenario, we'd like to see further clarification of this and why Potterton have done so
The Boys
OK, with the ring main connected to the CU, remove the other circuits one by one (connection by connection if you have to).
(Assuming you've not done so already)
And see at what point there is any change (If any).
Failing that, with all connected, break the ring at the sockets, one by one.
Don
OK, Dane:
You say the Ring tests fine when not connected to the CU?
You say Bonding removed for purpose of test?
Have you checked for continuity to another circuits CPC and or Neutral?
Don