how do i calculate 10kva so i can work this question out ?
a 3 phase 10kva transformer has a pf=0.9.calculate the line current for the transformer.
will i use sqaure root to work this question out ? are just x them all togeather?
I don't think you have enough information there, what voltage are you expected to use and is it star or delta configeration?
i take it is 50hz.i worded the question the way it is on the sheet.
frequency has nothing to do with this question - as above, we need more information to give you an answer
but at a quick guess, id say answer may be 13A?
16amps on the answer sheet.tryed some other questions and they did`nt work out but where close to what i got.
web site was swindon massive
16amps on the answer sheet.tryed some other questions and they did`nt work out but where close to what i got.web site was swindon massive
really need more info on this. even assuming PF of 1, i get 14.45A
BUT: if it was 10KW and not 10 KVA, i get 16A
so working on that
10/0.9 = 11.11KVA
......................................kVA X 1,000
Three-phase amps = -----------------------------------------
........................................ 1.732 X Line to Line voltage
so 11.11x1000 / 1.732 x 400
= 16A per phase
or, the even easier way
KVA / 0.692 = A per phase
so 11.11 / 0.692 = 16A
(the 0.692 is the 1000, 1.73 and 400 all into one number)
or at least i think this is right
P = √3 x VI x pf
V and I being line values
I = P / (√3 x V x pf)
Getting an answer of 16.04A
sorry, still don't see how you can calculate the current from the power with no voltage?
mickey-c could you show me how you got 16.04 I = P / (√3 x V x pf)
(√3 x V x pf) pf 0.9 what did you use for v