115V Stops Megger Testing Zs

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

paulcopeman

Active member
Joined
Mar 4, 2013
Messages
37
Reaction score
0
Location
romford
Hi.

I have been asked by a colleague that was carrying out a Zs on a lighting CCT what could be the cause of his megger not carrying out the test due to it only picking up 115v between phase and earth. He was doing 2 wire lo current loop test but meter just read 115v and bleeped apparently. I'll have to go and look tomorrow after I've finished my jobs but if I can point him in the right direction then maybe I won't have to go there.

I told him to go to board and link out phase and CPC for that CCT and do r1 +r2 but he hasn't got back to me today so I don't know how he got on.

 
Just finished my dinner. Thanks for your replies. I hadn't thought of dimmer switch. Yes it was taken at pendant.

If there was a floating earth then surely doing a two lead test (phase and CPC connected only) wouldn't have shown any voltage at all. My colleague got 115v apparently.

 
I hate to say it, but this shows how someone has "learned" to do the tests by placing probe A here and Probe B there, pressing a button and record the result. They probably have little understanding how the circuit really works and what they are really testing.

Did he repeat the test L-N? did he get the same result?

 
Sooty I'm fixing a fault on my van now. Busy life. I'm not sure what he has done . I'll have to find out tommorow.

More work for me.