paulcopeman
Active member
Hi.
I have been asked by a colleague that was carrying out a Zs on a lighting CCT what could be the cause of his megger not carrying out the test due to it only picking up 115v between phase and earth. He was doing 2 wire lo current loop test but meter just read 115v and bleeped apparently. I'll have to go and look tomorrow after I've finished my jobs but if I can point him in the right direction then maybe I won't have to go there.
I told him to go to board and link out phase and CPC for that CCT and do r1 +r2 but he hasn't got back to me today so I don't know how he got on.
I have been asked by a colleague that was carrying out a Zs on a lighting CCT what could be the cause of his megger not carrying out the test due to it only picking up 115v between phase and earth. He was doing 2 wire lo current loop test but meter just read 115v and bleeped apparently. I'll have to go and look tomorrow after I've finished my jobs but if I can point him in the right direction then maybe I won't have to go there.
I told him to go to board and link out phase and CPC for that CCT and do r1 +r2 but he hasn't got back to me today so I don't know how he got on.