Hi,
Got bit of a question...
Looked at a job (large takeaway shop)... They have a single 32A ring to cooking area - appliances (kebab, Bain Marie etc) are on plug tops...the twin surface skts are soon burning out - this must be due to the length of time the appliances are in use and the load the are drawing.
16A sockets seems a solution - but the ring is protected by a B32... With no 'plug top fuse', surely the device cannot be protected.
Just thought I'd ask incase could offer any advice.
Cheers,
Daz