Scenario - commercial property, out in the wilds. Pub / hotel.
Supply is 2 phase.
Pub have an online generator, powers up within 3 seconds on failure of mains.
The incomer is 250A per phase fuses L1 and L2, Into a main isolator ( not looked inside yet - interlocked.) - from there into a metering cabinet with Cts ( one red conductor, 2 black -70mm BS7889 in free space), and also into the generator housing ( BS5467 70mm singles, two red, one black.)
Back out of the same hole in the generator, and over to a Hager TPN DB ( there are 4 TPN boards on the premises - all different makes!, but NO polyphase loads.)
The Main Hager TPN DB has a 250A, TP switch disconnector, with L1 linked out to L3. The three TP submain DBs are fed from TP MCBs
Here`s the "big problem"
Because we`re only having 2 phase ( "split phase"), where the phases are 180 degrees from each other ( i.e. centre-tapped for N), we`ve got a phase-phase voltage of 480V
Hager main switch rated 415V, TP MCBs rated 400V
According to Hager & Merlin; their boards and breakers / disconnectors are only safe to a maximum of 460V. Obviously, if we allow the DNO`s 10% - we could be looking at 506V (460V +10%/-6%).
I`m thinking they`d be better with 2 DBs; each barred out to SP - so each board is only running 240V.
But the initial distribution of that, from this 3 wire 2 phase - unless I can get an enclosure, rated at say 600V, with a pair of single pole MCCBs?
I know Hager do NOT produce 600V rated switchgear for their TP DBs.
Anyone else ever had to deal with this issue? Its been installed for 10 years............
n.b. Install is shocking. Photos to follow in gallery - silicon around every cable entry top surface, BS951 used to terminate a SWA, 25mm tails damaged in enclosure by edges of front cover.
What a blinking mess!
Supply is 2 phase.
Pub have an online generator, powers up within 3 seconds on failure of mains.
The incomer is 250A per phase fuses L1 and L2, Into a main isolator ( not looked inside yet - interlocked.) - from there into a metering cabinet with Cts ( one red conductor, 2 black -70mm BS7889 in free space), and also into the generator housing ( BS5467 70mm singles, two red, one black.)
Back out of the same hole in the generator, and over to a Hager TPN DB ( there are 4 TPN boards on the premises - all different makes!, but NO polyphase loads.)
The Main Hager TPN DB has a 250A, TP switch disconnector, with L1 linked out to L3. The three TP submain DBs are fed from TP MCBs
Here`s the "big problem"
Because we`re only having 2 phase ( "split phase"), where the phases are 180 degrees from each other ( i.e. centre-tapped for N), we`ve got a phase-phase voltage of 480V
Hager main switch rated 415V, TP MCBs rated 400V
According to Hager & Merlin; their boards and breakers / disconnectors are only safe to a maximum of 460V. Obviously, if we allow the DNO`s 10% - we could be looking at 506V (460V +10%/-6%).
I`m thinking they`d be better with 2 DBs; each barred out to SP - so each board is only running 240V.
But the initial distribution of that, from this 3 wire 2 phase - unless I can get an enclosure, rated at say 600V, with a pair of single pole MCCBs?
I know Hager do NOT produce 600V rated switchgear for their TP DBs.
Anyone else ever had to deal with this issue? Its been installed for 10 years............
n.b. Install is shocking. Photos to follow in gallery - silicon around every cable entry top surface, BS951 used to terminate a SWA, 25mm tails damaged in enclosure by edges of front cover.
What a blinking mess!