AM2

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

retiredsparky

Member
Joined
Apr 15, 2009
Messages
39
Reaction score
0
The new am2 has four assessments[sections] A,B,C & D. Assessment A is further split into two sections A1 includes Risk Assessment and Safe Isolation of the rig assigned to you, time allowed 1 hour. Section A is your composite installation, time allowed 8.5hrs. Section B is, Inspection, Testing and Certification of your composite installation, time allowed 3.5hrs. Section C is again split into two, C1 safe isolation of the fault rig assigned to you and C fault diagnosis, time allowed 2hrs. Section D online multiple-choice exam, 30 questions in one hour, open book [bRB, OSG, GN3 & Electrical Installers guide to the buliding regs] 70% to pass.

Please note that the times have changed on some assessments [sections] therefore you are no longer allowed to go over time.

Candidates watch out for the following: safe isolation, not switching off main switch, label not attached, key left on show, not proving voltage indicator before/after the 10 tests.

Composite: Not installing the correct size cables, bonding connections/clamps loose, wrong type/current rating of MCB's installed, wrong fixings used on FP200, not wiring S-Plan to spec. functional not working.

Testing: not understanding the required tests, example not knowing how to prove polarity dead and live,how many test on a ring circuit, Ze test. How many test to be carried out for PFC. Certification: not completing all forms correctly.

Fault diagnosis, once again safe isolation has to carried out in the prescibed order, you are given 7 faults all wiring faults, only stating the type of fault and how to rectify.

Online exam as it is an open book should be passed without any problems.