Speaking to a colleague today -
This may have been because he just upgraded from DI to AC.......
Took the assessor to a CU change in a bungalow. Failed because he hadn`t de-rated the ring finals to 25A MCBs (cables in loft under insulation.)
He`s chasing around like mad, trying to find B25s to fit this Wylex board.........
The only ones I know of are the Eaton (MEM) ones; though I`m sure Hager do `em too.
Contactum don`t
Just beware - the area engineer thinks this is going to become more prevalent....
KME