Found During A Pir
NozSpark
Seaman stains™
May 28, 2008
12,316
122
North Wales Riviera
I carried out a PIR the other day and found this :eek:
This isn't the worst thing though.... This RCD was in a board thats fed off a 16mm T&E sub main,, only that it's not a submain,, the T&E was wired directly into the tails via henly blocks and burried in the wall
Thankfully I had a replacement RCD in the van (Merlin Gerrin), however it's installation has doubled the value of the crappy CGD 16th ED board - only 10 years old!!
I think that it was in the cage.... It was one of those preformed link bars..
Have to have a think how to sort it out,,, sub main will need RCD but then there are 7 circuits which won't have any RCD discrimination
Great having a spare to 'make fit'...
You know... I've got a thing about burnt neutral terminals (as per my last but few post).
I'm convinced there are more burnt neutrals than lives... but no-one knows why.
Maybe I need to get out more (or a holiday?...lol!), but I'm getting a bit OCD about it now...
?..........but no-one knows why.
Maybe you are getting. OCP?
I Had three jobs last week with burned out neutral,connections
Shower
Storage
400mm incomer to a server room MCCB
Just not quite understanding, but at the same time not caring
Canoeboy said:
None of you realise why the N burns out do you  ?   :slap
I find it quite steptoe to be honest :pmsl1:
FUC OFF    :red card
are you going to explain it? being the cleverer person you are,?
or does it need to be degrading coming from a numpty like me?  :|
It does always seem to be the Neutral but I have no idea why either.      Given the choice of yanking out a cable under load  I'd go for the L not the N .
Some say its these very hard copper cores  but its gone for years when they were soft copper.
Must to do with induction .
hi there
There is an increasing tendency for burnt out neutrals as we connect more and more it equipment in our homes and offices due to leakage !
Also ups systems cause these issues  this is usually eliminated by the use of harmonic filters in office block etc
but by the nature of pme systems etc the neutrals flow to other consumer units as well !
just a little thought for you to consider
cheers madfridge
hi there
cheers madfridge
:C   O)   :shakehead
Does it normally happen when 3-phase supplies are split to supply a single phase to 3 properties? The imbalance of the loads could cause high currents in the neutral leading to overheating at the terminals. the neutral terminal at the main switch could be the weakest point in the circuit also because of its design (not as sturdy as the meter terminals), the overheating and cooling causing mechanical stress to the joint and the neutral may not have been tightened as firmly as live and earth because it is deemed "less important".
I don't deal much with three phase.
Not really Rob, a 3 ph DNO supply split to 3 dwellings will simply be 3 off in number 1ph loads with Phase & neutral conductors sized according to the DNO rules, and, these days almost certainly a CNE conductor, so the N will be adequate for each loaded phase.
The days of the N conductor being smaller than the phases are long gone.
Ah yes,
diminished neutrals
Red white and blue instead of this new fandangled red tellow blue
Black plastic rawl plugs
Metal backboxes made from steel and NOT cheese
Terminals you could fit screws in
Ivory accessories
PYRO buried direct
Ricketts
Ringworm
Just reminiscing........NURSE! Can i have my special medicine please before I get meself settled for the night