TBHI maybe wrong but I get the impression that everyone is missunderderstanding the original post. Kung thought that by testing the circuit at 250v, then the 0.5Mohms reading was OK.I don't think he did ?
This is not the case. The circuit (if I read it correctly) is an LV circuit - 51v a.c to 499v a.c - and the insulation values given in table 61 of the bible are for the different voltage bands.
Because it is a 230v circuit, it should be tested at 500v d.c and the min. value of insulation resistance should be 1Mohm. However, doing a preliminary test at 250v d.c to protect the circuit STILL requires an insulation resistance of 1Mohm, not 0.5Mohm as has been suggested.
The 0.5Mohm value is only valid for a SELV circuit, regardless of the test voltage.
Which is what Kung said but he questions why the Nic bod said 0.71Mohm was a fail on SELV when 0.71Mohm is greater than 0.5Mohm?
Probably as clear as mud..Blushing
J
"The guy in the niceic dvd also on 'SELV' got 0.71M on '250V test' and said its of course a fail ! how come if its above 0.5M ?"Hi All Just a quick question on insulation resistance testing i know how to do it but what i dont get is i know its just an exam question and if you got readings like bs7671 further investigation would take place ie
250v------------->0.5M
500v------------->1M
etc
just been watching Niceic dvd and he gets >299M @ 500v & >99.9M @ 250v ! ive got a kewtech kt61 and mine wont give symbol > and how come in bs7671 the min is that low ?
The guy in the niceic dvd also on 250v test got 0.71M on selv and said its of course a fail ! how come if its above 0.5M ?
Regards
Kung.
I always do that but BRB does say can test at 250V instead of 500V if SPD equipment or other such equipment can not be removed but has to be at least 1Mohm not 0.5Mohm (612.3.2).Again I agree with the idea of testing with 250V first, if something is wrong or there is something still connected you will get a very low reading anyhow, if it reads above the max value for 250V (in my meter 200MOhm) I know that i can test with 500V without causing damage.
612.3.3 says that L+N to E is allowed. Why test E to L and E to N in this case as they will also be tested in L+N to E?The other acceptable way is to test E to L, E to N and than L+N to E.
I said that L+N to E is acceptable, but when you test this way how do you know that there is no problem between L and N? it does not have to trip the CB but still be too low to be safe. There for I always test all with 250 v and if the result is hight enough, I test with 500V.I always do that but BRB does say can test at 250V instead of 500V if SPD equipment or other such equipment can not be removed but has to be at least 1Mohm not 0.5Mohm (612.3.2).612.3.3 says that L+N to E is allowed. Why test E to L and E to N in this case as they will also be tested in L+N to E?
Ian.
I do what you do as well AK!Applaud SmileyI said that L+N to E is acceptable, but when you test this way how do you know that there is no problem between L and N? it does not have to trip the CB but still be too low to be safe. There for I always test all with 250 v and if the result is hight enough, I test with 500V.
And when it is a flex...? or the T&E is twisted? but is general I think that we agree...I do what you do as well AK!Applaud SmileyAlthough...
theoretically if there was a problem between L&N
On T&E it would show up between L+N & E because the E is physically between the L&N.
Obviously not true if singles or conduit wiring though!! :|
Ah!And when it is a flex...? or the T&E is twisted? but is general I think that we agree...