Following on from PK's high r1 but r1+r2 low thread,
http://www.talk.electricianforum.co.uk/question-answer-board/18307-electrical-installation-condition-report-r1-very-high-but-r1-r2-low.html#post245793
I was looking at a ring final circuit over the holiday week that has been in service
some 35 years. It is one of those where about half the sockets are spurs
and no tests were done when the board was changed in 2005. Some of the
reads are high at steps 2 and 3 in the sequence and Ze is no more than 0.2 Ohm.
When looking at it I found that there are no kitchen loads. That has its own ring.
In conclusion I thought the best thing to do was change the breaker from a B32
to a B20 or a B16 to give a higher allowable value of Zs. It only supplies light loads.
Do you guys have any other ideas? The thought of direct intervention to place
the sockets on spurs into the ring fills the householder with dread.
All else is OK with it.
http://www.talk.electricianforum.co.uk/question-answer-board/18307-electrical-installation-condition-report-r1-very-high-but-r1-r2-low.html#post245793
I was looking at a ring final circuit over the holiday week that has been in service
some 35 years. It is one of those where about half the sockets are spurs
and no tests were done when the board was changed in 2005. Some of the
reads are high at steps 2 and 3 in the sequence and Ze is no more than 0.2 Ohm.
When looking at it I found that there are no kitchen loads. That has its own ring.
In conclusion I thought the best thing to do was change the breaker from a B32
to a B20 or a B16 to give a higher allowable value of Zs. It only supplies light loads.
Do you guys have any other ideas? The thought of direct intervention to place
the sockets on spurs into the ring fills the householder with dread.
All else is OK with it.