Right, doing a supply for one of these as a favour so just want to ensure I am covering all the bases as not my normal type of work.

It needs a 16A supply.  Assuming it is a PME (Not seen it yet so assuming worst case).  SWA to rotary isolator.  The jacuzzi is to be treated as a swimming pool as in Section 702.  If the isolator is within 2M of the jacuzzi edge then it should be within a class 2 enclosure (702.55.4).  The supply must be RCD protected and if a PME requires an earth electrode if the switch is within 2M (702.410.3.4.3).  Am I correct in reading that if the switch is further than 2M then the earth electrode bonding is not required?  Assuming the main water bonding is satisfactory?

 
Last edited by a moderator:
Definitely not a bath - 702.11


Sorry I should expand.  Even if a bath is installed outside and has a jacuzzi as a part of it it should still be treated as a swimming pool as in the above regulation.

 
Unless things have changed with amd3 then the earth electrode is only a recommendation for any PME fed swimming pool installation. 

The recommendation is that an earth electrode of Ra<20ohm be installed and connected to the main equipotential bonding of the installation, ie connect it back to the MET.

quite simple really :)

 
Unless things have changed with amd3 then the earth electrode is only a recommendation for any PME fed swimming pool installation. 

The recommendation is that an earth electrode of Ra<20ohm be installed and connected to the main equipotential bonding of the installation, ie connect it back to the MET.

quite simple really :)


Yes.  But as I read it only if you have equipment within Zone 2?  If there is no equipment within that zone then am I correct in saying no earth rod required?

 
Yes.  But as I read it only if you have equipment within Zone 2?  If there is no equipment within that zone then am I correct in saying no earth rod required?