Right - lets see if I can help or confuse things some more.........We`re going to need supplies for bar equip, lights and possibly musicians equipment, so I intend to supply all three phases.

I`d prefer to have 3 X SP breakers; so 1 overload doesn`t take out all circuits.

The reason I don`t want the 30mA at the commando socket by the pub is that, if a piece of bar equip, or a musicians amp has a fault, we`d lose all power, and someone would have to go from the marquee to the main building to re-energise.

I`m thinking 100mA(T) at the building (if required) ; protect the outgoing flex with the PME. Drop the earth at the portable DB, and have a seperate plug/socket to connect to the (permanent) rod. The DB could then be fitted with RCBos (thanks Sidewinder ;) ) and everybods is happy??

Does that make things easier? I haven`t perused the BRB yet - thats tomorrow`s project.

KME
If you are going to have 100m A Time delay RCD AT SUPPLY END then I can see no reason why not to have ROD PERMANANT at Supply end and solve problem.

See BRB pG 196 Fig 709.2 3 Phase Plug and socket supply to Marinas.

Same set up wthout the Water :D

 
KME,

I think I have a solution that we can work between us.

You will need to be careful of earth zones from rods etc.

As I said in another thread I've just been throughn GN's 5, 7 & 8.

This is doable, you shoudl discuss the location of the marquees etc with the client and a few other things but I think it can be done.

I have also found a few specialist sockets for the trick connection, but as has been suggested the fault current rating of the sockets must be considered.

KME, ring me later if you want, I'm around online for a few hours, thus on the mobile, but I'll be in the factory tomorrow from about 07:30/08:00 till about 14:00. Mobile will be on as will laptop but I'm moving machines around!

 
K, but I have some "stuff" on 2moro till just after 12:00, no bother tho. you can also call down if you want & pick up some info that will clarify things, but I won't be able to call up with it.

Paul

 
I`ve got to go out in t`mornin anyway, so I can easily call down. You be in F`fach?

I`d just like to say:

Mr Andy (trademark)

Mr snakehips (sidewinder)

Mr lostit

Mr sparkyTim

Thanks for all your help & input guys, both on & off the forum :) :)