To unplug or not unplug

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Dave65

New member
Joined
Oct 6, 2022
Messages
1
Reaction score
0
Location
Devon
Someone I know recently had their fixed wiring tested and the ring main failed. However, it is PVC insulation and about 20 years old. The tester did not unplug the appliances and so surely this could affect the result. Also, the circuit was not disconnected at the DB and again wouldn't the adjacent circuits affect the result in some way? Thanks for any answers about this.
 
It is not a good idea, in fact a very bad idea, to try and do insulation testing with loads of stuff plugged in.

20 year old PVC installation can still have plenty of faults, or it can be absolutely perfect.
 
Appliances can affect results however I never unplug anything unless results are not what I expected. The circuit would have to be disconnected at the board to obtain the required test results.
 
edited that for you
Appliances only affect results if they themselves have inherent faults. I am referring to doing periodics generally in commercial and industrial environments with insulation resistance tests carried out to earth only. It is no different to subjecting an appliance to a PATest.
 
Well, I’m domestic usb sockets can give odd results and rcd sockets and fcus even more. Add in the cumulative effect of everything else and most circuits drop below sensible values, so unplugging is more often the case required
 
Well, I’m domestic usb sockets can give odd results and rcd sockets and fcus even more. Add in the cumulative effect of everything else and most circuits drop below sensible values, so unplugging is more often the case required
Modern rcd sockets and spurs yes but not a usb socket they should have no affect. I test large scale offices and only unplug if readings are not expected, drop to 250v when filtered extension leads are in use.
 
Well, I’m domestic usb sockets can give odd results and rcd sockets and fcus even more. Add in the cumulative effect of everything else and most circuits drop below sensible values, so unplugging is more often the case required
in theory LN-E testing should eliminate this. Personally I don't unplug these days, use LN-E and 250V, with the increasing numbers of plugged in items, USB sockets, cheap chinese products rated for 250V max, and other things that can skew results, as much I would prefer everything disconnected from the cct, in reality it is increasingly difficult to achieve, so I test accordingly.
 
Shouldn't we be doing a global test at the CU first.... rather than individual circuits?
(re chapter 3 guidance note 3)

Then break down individual circuits if readings are low?
 
Shouldn't we be doing a global test at the CU first.... rather than individual circuits?
(re chapter 3 guidance note 3)

Then break down individual circuits if readings are low?
Yes, that cropped up in a long discussion on here a while ago. I think it was @poni who pointed out that is actually what's written in the regs.
 