During a periodic inspection today come to testing a ring, L & N loop reading 0.56 & 0.57ohms... Thinking looking reasonable..
Then measure CPC.. readings bouncing around between 1000.0ohms and 1200.0 ohms.!!!!
Mmmm, thinks bit of a dodgy joint problem somewhere here..
Ask customer if any recent work....
Reply comes: Not since they moved in a few years ago, but the kitchen had been redone not long before they moved in..
I am thinking could be a Kitchen fitter created problem.. But NO.. I was proved wrong...
With all conductors disconnected at board, I wago together L-N-E at one end of ring.
With my 13A plug to meter lead adaptor I go round measuring 'L'->'N' and 'L'->'E', continuities at every socket I can find....
From the L->N readings I can suss out the socket wiring order..
and the L->E readings have some sockets less than 0.22 ohms and all the rest greater than 250.0ohms..
From the established socket order notes I had made, I open up the last of the low L-E reading and the first of the high L-E readings....
And low, it was beholdent unto me, that one of the old original sockets in the dining room... (Outside wall)...
Has mucho dampness issues AND, an interesting method of wiring CPCs...
Please NOTE:-
(Left Hand Cable) CPC onto socket E termination,
(Right Hand Cable) CPC onto metal back box lug. Also with a twisted joint if you look close.
So CPC continuity is via the socket to back box "corroded" fixing screws....
Me thinks the kitchen fitters should have noticed this whilst amending this same circuit in the kitchen??! :shakehead
As I am guessing this has been corroding for a few years now?
P.S.
Did a fix got my ring continuities back to:- L&N at 0.56ohms CPC at 0.91ohms
Guinness
Then measure CPC.. readings bouncing around between 1000.0ohms and 1200.0 ohms.!!!!
Mmmm, thinks bit of a dodgy joint problem somewhere here..
Ask customer if any recent work....
Reply comes: Not since they moved in a few years ago, but the kitchen had been redone not long before they moved in..
I am thinking could be a Kitchen fitter created problem.. But NO.. I was proved wrong...
With all conductors disconnected at board, I wago together L-N-E at one end of ring.
With my 13A plug to meter lead adaptor I go round measuring 'L'->'N' and 'L'->'E', continuities at every socket I can find....
From the L->N readings I can suss out the socket wiring order..
and the L->E readings have some sockets less than 0.22 ohms and all the rest greater than 250.0ohms..
From the established socket order notes I had made, I open up the last of the low L-E reading and the first of the high L-E readings....
And low, it was beholdent unto me, that one of the old original sockets in the dining room... (Outside wall)...
Has mucho dampness issues AND, an interesting method of wiring CPCs...
Please NOTE:-
(Left Hand Cable) CPC onto socket E termination,
(Right Hand Cable) CPC onto metal back box lug. Also with a twisted joint if you look close.
So CPC continuity is via the socket to back box "corroded" fixing screws....
Me thinks the kitchen fitters should have noticed this whilst amending this same circuit in the kitchen??! :shakehead
As I am guessing this has been corroding for a few years now?
P.S.
Did a fix got my ring continuities back to:- L&N at 0.56ohms CPC at 0.91ohms
Guinness