DONT STAY LURKING AS A GUEST,
CLICK HERE TO JOIN.
John cullen
TT system
John cullen
Hi guys is it ok to do the Zs=Ze + R1 R2 calculation on a TT system. I got a reading of 20.3 ohms on the Ze and .55 on a radial socket circuit. So how does the equation work.
john
Share this post
Link to post
NozSpark
The calculation doesn't take into account any parallel paths through the bonding conductors... remember that the same services could be bonded next-door and be part of a TNS or TNCS installation
Share this post
Link to post
Onoff
Just don't forget to reconnect any bonding conductors removed for testing!
Share this post
Link to post
John cullen
So essentially you can’t add the Ze and the R1 & R2 together??
Share this post
Link to post
Rob.
This will give you the worst case scenario.
An if there wasn't any extraneous parts it would work out. Remember if it has metal water an gas services. An they are bonded, they are in effect 2 giant additional earth rods.
Share this post
Link to post
binky
In theory on a 30mA RCD max Zs could be 1667 Ohms. However to me that means a cct / earrh rod is buggered somewhere! So on TT I work on the basis that R1+R2 values should be as per house with suppliers earth. Rod should be less than 200 Ohms - recomended figure for a stable earth, so as you have done above add your Rod to your R1+R2 figures to give you Zs.
Share this post
Link to post
John cullen
Cheers mate
Share this post
Link to post
Andy™
you can calculate Zs by Ze + R1R2 (you can also do the same on TN systems)
Edited by Andy™
Share this post
Link to post
Create an account
Register a new account
Sign in
Sign In Now