SWA termination

Recommended Posts

Traineeboy

If you have a 10mm2 SWA that needs to come back to the main consumer unit but it would be a nightmare to gland into the consumer unit because it only has the Hager Square knock outs - would it be acceptable to terminate the SWA into a switch fuse then run a 10mm2 T+ E back to the board on a MCB.

 

I know it's probably best to do a submain  via Henley but is there anything wrong with doing it the way above. The SWA supplys a mini RCD unit in a shed so my thinking would be that the 10mm2 T + E from the switch fuse to the house consumer unit would’nt need RCD protection as the T+E would be clip direct and the SWA from the switch fuse to the shed is mechanically protected.

 

Thoughts?

Share this post


Link to post
Share on other sites
steptoe

Be aware of the earth sizing. 

I wouldn't worry about the RCD bit as long as it's surface, but a bit of 10mm earth may be a good investment, 

You could just use a metal adaptable box , stuffing gland, etc, 

There is a picture somewhere of where my actual house supply/submain changes from tails to 16mm SWA via ISCOs and an adaptable box. 

Share this post


Link to post
Share on other sites
Traineeboy
6 hours ago, steptoe said:

Be aware of the earth sizing. 

I wouldn't worry about the RCD bit as long as it's surface, but a bit of 10mm earth may be a good investment, 

You could just use a metal adaptable box , stuffing gland, etc, 

There is a picture somewhere of where my actual house supply/submain changes from tails to 16mm SWA via ISCOs and an adaptable box. 

 

Thanks, of course a 10mm2 earth from the switch fuse to the main consumer unit earth bar. I hear you about a metal box and could do that below the consumer unit to cover the square knock out. I know inside the adaptable box I could just bring the SWA cores through but if I wanted to join SWA to T + E without a switch fuse what's the best product to do that? 

 

Share this post


Link to post
Share on other sites
Andy™

if its a small cable, like 4mm and less, you can use a galv conduit through box. larger and youll need a metal enclosure or similar to gland into and have enough space for terminations. you can get 100x100x50 metal enclosures fairly easily

 

can you not just make a round hole into the consumer unit though and gland it into there? and also look for SWA earthing nuts, far better than a banjo on some enclosures, especially into plastic boxes

Share this post


Link to post
Share on other sites
binky

Have done this many times, but I usually use a plastic box. I don't normally fit a switch fuse if tapping into a spare way in the board. 

Share this post


Link to post
Share on other sites
Fleeting

If it is close to the board I would use 10.0 6181Y and a 10.0 cpc then it is a case of like for like csa and crimps and you don't have the bother of the 4.0 cpc from the T&E.

Share this post


Link to post
Share on other sites
SPECIAL LOCATION
5 hours ago, Traineeboy said:

 

Thanks, of course a 10mm2 earth from the switch fuse to the main consumer unit earth bar. I hear you about a metal box and could do that below the consumer unit to cover the square knock out. I know inside the adaptable box I could just bring the SWA cores through but if I wanted to join SWA to T + E without a switch fuse what's the best product to do that? 

 

 

You can get boxes that come with terminals suitable for you to join 10.0mm conductors..  

e.g.

https://www.screwfix.com/p/ip65-57a-11-terminal-weatherproof-outdoor-adaptable-box-140-x-79-x-140mm/13096#product_additional_details_container

 

or if you want a bit more room 16.0mm terminals...  

https://www.screwfix.com/p/ip65-101a-24-terminal-weatherproof-outdoor-adaptable-box-180-x-91-x-180mm/18734#product_additional_details_container

 

Guinness

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.