10mm

Link to comment
Share on other sites

hmmm i'm under the impression its not that clear cut Apache

maybe so. I will be interested to see. Ok I'll ask what the earthing arrangement is?

Link to comment
Share on other sites

Table 54.8 would disagree with that and support Patch. Neutral is 35mm or less, then 10mm. Check out BRB pg 134.

Link to comment
Share on other sites

pme

Table 54.8 page 134, bottom part of reg 544.1.1

C.S.A. of supply neutral 35mm or less

minimum C.S.A. of main bond = 10mm:D

Link to comment
Share on other sites

quote "buried earthing conductors must be atleast: 16mm copper if not protected against mechanical damage but protected against corrosion

"

?

Link to comment
Share on other sites

quote "buried earthing conductors must be atleast: 16mm copper if not protected against mechanical damage but protected against corrosion

"

?

when did we bury anything?

Link to comment
Share on other sites

quote "buried earthing conductors must be atleast: 16mm copper if not protected against mechanical damage but protected against corrosion

"

?

"EARTHING"

not

"BONDING"?;)

Link to comment
Share on other sites

The Don's boys have to bury horses without heads all the time ;).

No they don't. Ever wondered what goes into to a hot dog and those fishshop 'sausages'?

Link to comment
Share on other sites

The Don's boys have to bury horses without heads all the time ;).

Applaud SmileyApplaud SmileyROTFWL

Link to comment
Share on other sites

So the important thing - I was right all along ;)

Link to comment
Share on other sites

"EARTHING"

not

"BONDING"?;)

Well it is in note 3 of table 4.1 in OSG referring to bonds. Guess its if you need to get from one place to another and have to bury the cable (e.g. under a door step).

Link to comment
Share on other sites

No they don't. Ever wondered what goes into to a hot dog and those fishshop 'sausages'?

No I haven't for that very reason.

Link to comment
Share on other sites

Well it is in note 3 of table 4.1 in OSG referring to bonds. Guess its if you need to get from one place to another and have to bury the cable (e.g. under a door step).

buried means either surely?