trevor_clark
New member
thanks to all the guys that gave advice, found it most helpful, will be going down the split meter tails & mini CU route.
regards
Trevor
regards
Trevor
Hi Prodave,Just to add to the above, it's because when someone gets a shock and the RCD trips, the Solar PV inverter will continue providing power for up to 5 seconds before it detects loss of grid connection and shuts down. By which time your poor victim is probably dead.
Sadly it seems a lot of Solar installers just don't understand this.
This is one of these moments in life, when one has what you would term an epiphany. With Andy's and Prodave's comment and explanation I now fully understand the problem and regulation. If you know why something is written then you fully understand it.712.411.3.2.1.1 - must be on supply side of any protective device for ADS of other circuits (short text of it)
about as clear as you can possibly get it, yet the monkeys who install it still ignore it...
Hi Sidewinder,
In Northern Ireland it is common to fit panels on a shed, which is fed via a sub main from the house. And that sub could be backed up by an RCD. Effectively then this would be a no no... yes?
even if it will trip within 5s, it still doesnt comply with 712.411.3.2.1.1As to the submains, I suppose you could look at the actual disconnection time - likely to be 0.1sec if MCB, look at the inverter specs, find out the actually shut down time (which might be significantly below the 5s the standard requires) add these together and if you are still less than 5s required for the submain circuit then there isn't a really a problem.
Ker pow Phoenix is correct. If you drive this imaginary nail into a wire and the RCD trips, the inverter then becomes electrically separate so you cannot get a shock to earth. I wonder is why this regulation 712.411.3.2.1.1 is effectively ignored by the industry perhaps,,, :innocentAs to the RCD issue, I am with the majority regarding the fact that it should not be read from the same RCD as other circuits. (however there is a bit of a saving grace in that when the RCD trips * that the suppliers N-E link is gone and the inverter is basically a separated IT system until it shuts down)
why not swop main switch RCD for a main swith and add RCBOs for circuits you need 30mA protection on, or meter tail blocks and Mini CU for solar.
what's your house supply on earthing wise
There is no FIT here, just the free energy. It is standard to Irish which is more or less the same as the UKYou need to look at the required disconnection times, and see if the circuit protection on the DNO supply, and the micro generation supply both meet the requirements for BS7671, and compare these with those documented for the inverter.
Also, if you are going for FIT, you need to consider the requirements for that also.
I don't know the scenario you have to say from here.
thats a big ifKer pow Phoenix is correct. If you drive this imaginary nail into a wire and the RCD trips, the inverter then becomes electrically separate so you cannot get a shock to earth. I wonder is why this regulation 712.411.3.2.1.1 is effectively ignored by the industry perhaps,,, :innocent
The house, in Ireland, is a bastardised TNCS which they call a ' neutralized supply' with an installation earth rod fitted. Don't fancy a mini cu and I cannot afford RCBOs :facepalm: