just been today to look at a 50Kw 3ph solar PV,
backfed from the sub DB in what I am guessing to be a 35mm 4c SWA,(possibly larger), but I have calc'd on 35mm, its close on 140M so do I work out VD at 8% as its a private supply, or 5% as it connected to the public network? either way I think Im inside anyways, can someone confirm please?
Im not 100% sure on this either, but I think Im going to have to downgrade to 63A in order to get this through,,,,,,,,,
I dont think it will pull anything any bigger, I havent even bothered to work this bit out yet as my head is ****ted with a load of other stuff, so I just wanted to think aloud so to speak in case I have missed something totally obvious and am wasting my time even working anything else out.
thanks.