Cable calculation
Dec 6, 2020
13
Hi All,
I am very rusty on cable calculations as I haven’t really needed to do it very often and kind of need a bit of reassurance.
I need to supply a 3 phase sub board, 45 meter run in a duct from one switch room to another.
main supply is 100Amp
Sub board is a 3 phase 100Amp main switch
I was thinking I would need 35mm SWA 4 core with 20mm separate earth. Does that sound correct.
Any help is appreciated.
To be honest I don’t know the Ze
it is in a duct under ground with 5 other SWA
Ambient temp 30
😵 10mm sounds like he is penny pinching!
Hi m8,
it’s 100Amp main switch
a sub contractor installed a 16mm SWA for this already but it has been flagged that it is too small.
they now want the cable calculation. This is what I am struggling with.
cheers
Hi m8,
cheers
I was replying to kerching
I would have said 16mm would not have been big enough h to start with from. Day 1 as I'd have said min 25mm ideally 35mm due to possible. Load at 100 Amps I would have to do a calculation but I'm out at the moment
It’s the calculation part I’m not confident with. I would think a 35mm 4 core would be fine. If you can help me out with the calculation when you have time that would be great. 👍👍
My thoughts exactly...can't get him to understand that he has used thermosetting ratings BUT his terminals are not 90° so he needs to derate to PVC ratings....anyway, not my monkeys, not my circus
I wouldn't have put 63 amps onto a 10mm in any case I'd have upped it from a safety sizing POV to be on the safe side at that level of current and protection.
Hi Badger
Would you have any time to help me out with this calculation?? Like I said I don’t have the Ze but just an idea would be helpful. Cheers
Load?
Earthing arrangement?
PFC?
Ze/Ra?
Distribution or final circuit?
Any lighting?
Installation method?
Load?
PFC?
Ze/Ra?
Any lighting?
The load is 100Amps
just now the board is on a TT
but I can run an earth in with the new SWA
Ze 0.08
its in a duct buried
45 meter run
all that we are putting onto this board is 6 car charging points
6 x 32Amps
Using 50mm CSA 70c SWA I get VD of 3.6 using the resistive load column.
R1+R2 of 0.034 ohms giving Ze of 0.114.
PFC 4.95Ka.
Adiabatic has 1.06mm for copper and 2.40mm for steel armour for a 5 second disconnection time.
Thanks for that Sidney, it’s appreciated.
I got to say I didn’t think it would be a 50mm SWA. Don’t know if I would get that through the duct🙈
35mm is only good for 98 amps buried direct for three phase.