How Do I Know If A R2 Reading Is Correct

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

garaoke

Member
Joined
Jun 27, 2013
Messages
5
Reaction score
0
Location
ayrshire
I got a electrical test to check ze was .18 zs was .4 for a cooker circiut of length 1m. R2 was .00 on test sheet, also a ring main of 20m r2 was .05 I thought no chance as r1+r2+ze would not work out any info guys

 
So the ring main of 20m at .05 ohms is defo wrong

So the reading of .05 for the ring main is defo wrong

 
From my calcs a 20 mtr 2.5mm R1 should be 0.15 ohms, or thereabouts and the R2 1.5mm CPC 0.25 

 
Last edited by a moderator:
From my calcs a 20 mtr 2.5mm R1 should be 0.15 ohms, or thereabouts and the R2 1.5mm CPC 0.25 
If it's a 20 M Ring final, then the end to end resistances are as you state.

But R1 and R2 will in fact be half that due to two cables in parallel (strictly speaking it will depend on where on the ring you test)

That's why the figure of 8 test was devised, that should give the same reading wherever you test on the circuit.

 
I stand corrected

what I should have more correctly stated was that the END TO END continuity readings for the L and the CPC on a 20 mtr Ring Final Circuit would be expected to be in the region of those values.

Added together and divided by four will give the expected R1 + R2 value that should be confirmed by the cross over method

(L of cable one connected with CPC of cable 2 and L of cable 2 connected with CPC of cable 1 and measure the continuity between the two )

Thanks Dave

 