INSULATION TESTING ON 3 PHASE BOARD

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

speedster

Member
Joined
Nov 12, 2010
Messages
71
Reaction score
0
Location
Somerset
Hi All. I was wondering how others do insulation testing on a 3 phase board,in particular,Neutral to Earth and Phase and Neutral combined to Earth.The problem of course is that on a TN-C-S the Neutral and Earth are combined at the intake position.If there is a 4 pole isolator,the neutral can be isolated,so no problem but most isolators are 3 pole.I did one the other day and disconnected the Neutral inside the board,But I'd like to know how others do these tests.

Thanks,

Speedster.

 
Hi mate,

There should be a test link on the neutral bar, inside the board - disconnect it (after safe isolation)

I'd disconnect it carefully, then re-test N-E with your voltage tester (the 11th test for safe isolation)

After that, do your normal 10 point IR test or, if you need to test Line/Neutral connected together to earth, croc clip the busbars and neutral.

MCBs closed, either way - and don't forget to re-instate the test link:D

 