New member
Hi all.
i recently asked this on a screwfix forum, but unfortunately only got one response. With due gratitude to that person I wondered if there were any other opinions?
I am considering the electrical and builders work implications of a domestic kitchen refurb which is presently in the planning. I have limited space for expansion in the consumer unit so need to keep this in mind. The kitchen will have a ring main for countertop sockets. Additionally I anticipate a 32A 6mm2 T&E radial to the 7.5kW induction hob.
Under the countertop is arranged two single multifunction ovens (3kW + 3.5kW) and two compact multifunction ovens (combi steam and combi micro (3kW + 3kW). The manufacturers info states minimum 16A fuse connection on each appliance. The ovens are arranged horizontally side by side in a group. With diversity in mind is there are reason why the four ovens should not share a single 32A 6mm2 radial with single above counter DP switch continuing with a drop to four individual connection units behind the four appliances? Thanks in anticipation
i recently asked this on a screwfix forum, but unfortunately only got one response. With due gratitude to that person I wondered if there were any other opinions?
I am considering the electrical and builders work implications of a domestic kitchen refurb which is presently in the planning. I have limited space for expansion in the consumer unit so need to keep this in mind. The kitchen will have a ring main for countertop sockets. Additionally I anticipate a 32A 6mm2 T&E radial to the 7.5kW induction hob.
Under the countertop is arranged two single multifunction ovens (3kW + 3.5kW) and two compact multifunction ovens (combi steam and combi micro (3kW + 3kW). The manufacturers info states minimum 16A fuse connection on each appliance. The ovens are arranged horizontally side by side in a group. With diversity in mind is there are reason why the four ovens should not share a single 32A 6mm2 radial with single above counter DP switch continuing with a drop to four individual connection units behind the four appliances? Thanks in anticipation