Power Ball
Senior Member
Can you guys give me some advise please, I went to look at a job yesterday and basically it is a small cottage with a 6 way Wylex re wireable cu on econ seven for night storage heters and a 6 way Wylex to control his 2x light radials 2x sockets rings 1x cooker 1x immersion heater.
Both are fed from a henley block to split the incoming tails
I have been asked to upgrade as the guy is looking to let the ptoperty.
Room on the board is at a premium.
Should I leave the econ seven cu alone and change the domestic cu ?
As I only have 10" room for new cu I can only think to use either 10" enclosure with main switch and 6 RCBO's or would it be ok to use a 10" enclosure with a RCD as the main isolating swich with 6 MCB's ( would this be going back to 16th edittion) + all mcb's would be coverd by the same RCD
Earthing is supplied by a TT rod
Is there a more effective way to do this and keep within the regs...
Any ideas would be greatly appreciated
Many thanks
Chas