Lighting Contactor

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Elekk

Senior Member
Joined
May 26, 2010
Messages
108
Reaction score
0
Can someone give me a link that shows the wiring diagram to wire three 4-pole lighting contactors in parallel (to control 12 lighting circuits.)

 
Elekk,

IF you are merely switchitn lives, run the lives through the load connections.

IF you are using a "normal" light switch to control the contactors, you don't need a retain circuit, thus wire all the A2's in parallel to N.

Wire the A1's in parallel, with the light switch in series with the supply to one of them

HTH

 
contactor.jpg
 
;)

ignore the aux contact :Blushing

thanks button bottom right :coffee :D

 
Thanks for the information Lee. One more question about the circuit that you posted above; Can this circuit be used for "four" 3-phase lighting circuits, or "twelve" 1-phase lighting circuits, or both?

 
Elekk,

This would depend on the rating of the contactor.

IF the load contacts were 4 off full load rating then you could use them for 12 lighting circuits, if not then you could only use the 4th contact to its rated current.

4 (load) pole contactors are freely available, and these may also have another aux contact.

 
My example was using 3 pole contactors . So yes 4 3ph supplies or 12 1ph

 