Swapping an MCB

Recommended Posts

stevesown

Hi all,

I have a customer with a metal box type Wylex consumer unit, which presently has a NHXSBSB16 breaker feeding a small pump set which is just fed Direct Online.

I need to swap to a Type C breaker as the new pump set is powered by variable speed drives.

The question I need answering is:- Can I put just a normal type C breaker in the consumer unit?  as the RCBO types normally trip when you connect variable speed drives due to the characteristics within the drives.

Share this post


Link to post
Share on other sites
ProDave

Why do you think you need a type C for a VSD?  They almost always have soft start.  If anything it would be the DOL pump that would need the type C

Share this post


Link to post
Share on other sites
Rob.
4 minutes ago, ProDave said:

Why do you think you need a type C for a VSD?  They almost always have soft start.  If anything it would be the DOL pump that would need the type C

 

VSDs need to charge their DC bus capacitors and as such have a large inrush current when the VSD is first powered up. 

Share this post


Link to post
Share on other sites
stevesown

Hi Dave thanks for the reply, In my years of experience, I always tend to have problems with Type B on all installations weather VSD or DOL, so I normally change them as a matter of course.

My main question is, is it OK to remove the RCBO & change it for a normal MCB on the Wylex metal box consumer unit?

Share this post


Link to post
Share on other sites
Andy™

may... maybe not. if the circuit doesnt need RCD protection and your cables sizes / zs are OK for a type C then yes. otherwise no

Share this post


Link to post
Share on other sites
Evans Electric

Isn't there some bumph about  creating a " Risk assessment"  to  avoid the use of an RCD  ?  

Share this post


Link to post
Share on other sites
binky
1 hour ago, Evans Electric said:

Isn't there some bumph about  creating a " Risk assessment"  to  avoid the use of an RCD  ?  

 

Yes, you can omit things provided you can justify your actions, and to do that your need a Risk Assessment. For Example.,I much prefer not to RCD my solar circuits for various reasons to do with reliability - RCDs dont like the way inverters start up and shut down, not usually an issue, but with some makes a total pita! I can justify this on the grounds my cable runs are usually surface / buried more than 50mm, and I don't fit sockets under the panels :D

Share this post


Link to post
Share on other sites
Evans Electric

What does one actually  do with the Risk Assessment ?     Send copies to your MP ,  the NICeic ,  Building Control , The Queen  ?  

 

I've only ever done any twice ,  to  Project Managers .   

Share this post


Link to post
Share on other sites
ProDave
1 hour ago, Evans Electric said:

What does one actually  do with the Risk Assessment ?     Send copies to your MP ,  the NICeic ,  Building Control , The Queen  ?  

 

I've only ever done any twice ,  to  Project Managers .   

File it so you can present it in court IF the smelly stuff hits the fan.

Share this post


Link to post
Share on other sites
Murdoch
2 hours ago, Evans Electric said:

What does one actually  do with the Risk Assessment ?    

 

I've never done one ....... so I suppose the logical answer is send a copy with the certificate and file a copy so your CPS can view it.

 

 

Share this post


Link to post
Share on other sites
Evans Electric

How do they know you only just wrote it down ?    

 

NIC Man      "Oh my goodness you havn't fitted an RCD to this circuit " 

Me                  " Ah  but I wrote it on this piece of paper " 

NIC Man       " Thats OK then  " 

 

 

The last ones I did were for a Project management  team . 

Q .  Will your operatives be working at  height  .

A.   Yes from a mobile scaffold tower .

Q.  What precautions will you take to prevent a fall?

A    We will be very careful .   

Share this post


Link to post
Share on other sites
Evans Electric
2 minutes ago, Murdoch said:

 

I've never done one ....... so I suppose the logical answer is send a copy with the certificate and file a copy so your CPS can view it.

 

 

I honestly don't think they'd welcome it Murdo  . 

 

I've said this before but I keep wondering if all the local building control departments now all have a database  of all the electric jobs carried out  since  Part Pee  came in .   And would they be willing to search it for , say , a house buyer  who wants to know when it was rewired & by whom. 

Share this post


Link to post
Share on other sites
Blue Duck
13 minutes ago, Evans Electric said:

How do they know you only just wrote it down ?    

 

NIC Man      "Oh my goodness you havn't fitted an RCD to this circuit " 

Me                  " Ah  but I wrote it on this piece of paper " 

NIC Man       " Thats OK then  " 

 

 

The last ones I did were for a Project management  team . 

Q .  Will your operatives be working at  height  .

A.   Yes from a mobile scaffold tower .

Q.  What precautions will you take to prevent a fall?

A    We will be very careful .   

 

 

Working off a scissor lift in a  supermarket warehouse, site manager asks us what is our escape plan?

I told him we would jump off onto that pallet of toilet roll.

 

Not amused

....

 

 

:lol:

Edited by Blue Duck

Share this post


Link to post
Share on other sites
Evans Electric

Imagine a laughing  smiley face . 

Share this post


Link to post
Share on other sites
Murdoch
39 minutes ago, Evans Electric said:

I honestly don't think they'd welcome it Murdo  . 

 

 

I find they struggle to ask sensible questions ......... so insisting on seeing such documents is surely something they want to see.

 

Last Stroma inspection they wanted to see my "complaints procedure" - a written copy - I said I don't get complaints - I don't think the assessor thought my response was suitable!

Share this post


Link to post
Share on other sites
kerching

Risk assessment?

try doing one for a diving course with a projected depth of 75m!

 

risk......death

cause....running out of gas and/or drowning

method of risk reduction.....stay in Pub

Share this post


Link to post
Share on other sites
Bruspark
1 hour ago, Murdoch said:

 

Last Stroma inspection they wanted to see my "complaints procedure" 

Is he back at work yet ? 

Share this post


Link to post
Share on other sites
binky
45 minutes ago, kerching said:

Risk assessment?

try doing one for a diving course with a projected depth of 75m!

 

risk......death

cause....running out of gas and/or drowning

method of risk reduction.....stay in Pub

Probably goes down as well as "I'm 54 and still alive with every intention of reaching retirement"  :^O 

Share this post


Link to post
Share on other sites
Sharpend

I think we all have to do a mental risk assessment everyday in this day and age,

 

if I make it too work and back without getting mugged, stabbed or shot at then I consider myself to have passed and the risk assessment was successful. 
 

:coat 

Share this post


Link to post
Share on other sites
NozSpark
4 hours ago, Evans Electric said:

I honestly don't think they'd welcome it Murdo  . 

 

I've said this before but I keep wondering if all the local building control departments now all have a database  of all the electric jobs carried out  since  Part Pee  came in .   And would they be willing to search it for , say , a house buyer  who wants to know when it was rewired & by whom. 

 

I know that the NIC do (well, the notified ones....... )

http://www.checkmynotification.com

Share this post


Link to post
Share on other sites
Sidewinder

Just remember if you are doing RA’s as part of your design, make sure that your insurance covers that aspect of your work.

A lot of “normal” electrical contractor policies won’t.

For industrial or commercial work, this RA it down to the “Duty Holder” for the premise under EAWR.

If, you as a contractor do the RA, then you provide that as a consultant, & you need to be sure that you are covered, otherwise if things go wrong, it’s you that will be sought out.

Share this post


Link to post
Share on other sites
binky

would that be covered by Indemnity Insurance?

Share this post


Link to post
Share on other sites
Sidewinder
59 minutes ago, binky said:

would that be covered by Indemnity Insurance?

Only if you have specifically included it by telling them that you are going to be doing it, and you have provided evidence of competence, or not to allow them to evaluate the premium as to whether you are competent to give that advice or not.

Share this post


Link to post
Share on other sites
Murdoch
3 hours ago, Sidewinder said:

Just remember if you are doing RA’s as part of your design, make sure that your insurance covers that aspect of your work.

A lot of “normal” electrical contractor policies won’t.

For industrial or commercial work, this RA it down to the “Duty Holder” for the premise under EAWR.

If, you as a contractor do the RA, then you provide that as a consultant, & you need to be sure that you are covered, otherwise if things go wrong, it’s you that will be sought out.

 

"informative"

 

Yet some BS references suggest we should be doing them ................. and I doubt many people realise the impacts of doing them and getting them wrong!

Share this post


Link to post
Share on other sites
Sidewinder

If you look at BS7671, you will also see “normative” & “informative” appendices,

Normative appendices have as much relevance as the main part of the standard.

That is another thing that many miss!

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.