appendix 15 page 362if its what i think your saying then its no different than a spur at the origin which is in brb somewere.
if its what i think your saying then its no different than a spur at the origin which is in brb somewere.
Disagree; and here`s why:appendix 15 page 362
agree. doing a pir you'd spot that a mile offDisagree; and here`s why:You don`t have a ring and a spur, you have 2 radial ccts, on 2.5mm, protected by a 32A OCPD.
It doesn`t comply. Pure & simple. Sorry, I`m with the technical dept. on this one.
Even if it didn`t contravene a reg, I`d consider it bad practice.
KME
but its allowed. overload can be omitted at start if its provided elsewhere or the load cannot create an overload.Im with KME on this,you have 2 radial circuits wired in cable that can only carry 27A and protected by a device that is larger.
cable > protective device > design current
basic stuff really
this has nothing to do with a ring. the fact is, the cable is protected against fault current by RCBO. its protected against overload by SFCU. it does not contravene any regs. the design is fully compliant with 7671its not really the same as taking a 1m spur off a ring in 1.5 for a FCU to the alarm though is it,the circuit has been designed in a poor manner to start with.
I would almost go as far as to say the design does not comply with BRB.
neither is a ring main with a spur when someone adds another outletThe cable isn`t protected against overload if someone adds a double socket to it.chapter 1. BRB