Hi Chaps been a bit busy waiting for phone calls lately so sorry for not visiting.
I am a bit confused doing two small extentions at the moment they are back to back, one house is pme the other as far as i can see is tt but i cant find an earth stake outside. Quick Zs reading taken from socket in the pme house 0.26 all o.k.Same test in tt house first reading 100 ohms (indicating tt) later on did test again without changing anything, reading obtained 0.56 hence my confusion!.
I am wondering if i am getting something coming from next door via water pipe ect.My main question is do i phone the electric supplyer or the DNO ? and should i ask them to pme the tt house or would you suggest i fit a new earth stake and keep it tt.do they charge to upgrade to pme?
I am always grateful for all your responses many thanks in advance ssab. ?:| ? :|
I am a bit confused doing two small extentions at the moment they are back to back, one house is pme the other as far as i can see is tt but i cant find an earth stake outside. Quick Zs reading taken from socket in the pme house 0.26 all o.k.Same test in tt house first reading 100 ohms (indicating tt) later on did test again without changing anything, reading obtained 0.56 hence my confusion!.