Quick question I have fitted a shower 9.5kw I have an old fuse board with a 30amp rewireAble fuse with a 6mm out to a rcd unit 63amp rcd and a 50 amp mcb when I turn the shower on it trips the rcd straight out any help would be greatly appreciated!
I am seriously worried if this is the quality of training nowerdays...
From your thread on here...??
You have had proper C&G training?
http://www.talk.electricianforum.co.uk/electrician-talk-forum/19849-17th.html
Back to basics..
If a circuit has been correctly tested BEFORE energising an and RCD that has been tested (off load) as working correctly..
Then the ONLY reason the RCD would trip would be that the appliance connected is faulty...
But if you say it is a new shower..?
either you haven't done the basic tests as wot you should have learned at college
or you have messed up the installation somewhere!!
1/ What are your R1+R2 readings?
2/ What is the Insulation Resistance reading of the cable?
3/ What are your RCD test times?
4/ Have you confirmed you are going to comply with volt drop on your 6.0mm??
5/ What cable and MCB rating do the manufactures instructions suggest?
6/ WHAT is the point in wiring a 50amp MCB off a 30amp 3036??
7/ Notifiable work maybe????
Any answers to the above may help us to help you..