Found the previous periodic test sheet today in a property. The property is a ground floor unoccupied flat in a 3 story block, with no gardens. All very simple.
Page 1. Shows "unsatisfactory" yet on page 2 "satistactory" is shown.
Page2. One of the listed faults was " all circuits have 3871 typ2 MCBs in use" code 2
Also " No neutral continuity on the socket circuit" code 3, No RCD protection code 2, 240v fan above bath code 4.
Page3. The cert was only valid for 1 year yet (2 years ago) no'one has ordered a new cert to be issued
It was given 1 year "provided that any items given a code 2 must be remedied without delay. 2 years later and still no RCDs etc.
TNS ticked when it is TNCS
U1 230v Uo 240v
Ze 0.2 when it is 0.07
1361 Main fuse at a supposed 60A, yet he has put 100A as Max demand in a 1 bedroom flat with no shower.
Water and Gas bonds both ticked.
When i looked neither were connected and no evidence of ever being connected just stuffed in long lengths behind units and gas pipe boxing. (all kitchen and boiler work was done prior to the test.)
Means of earthing
Distributors facility ......N/A, Installation earth electrose........N/A
Page 4 (tick sheet)
Basic protection...obsticles Y...Barriers Y..placing out of reach Y
Fault protection
Prescence of earthing arrangements for combined protective and functional purposes ....y
Electrical separation
for MORE than one item of equipment...Y
Presence of diagrams...Y
Labelling of protective devices...Y (Even though an MCB is still labelled as immersion when it has been removed and replaced with a combi)
Presence of undervoltage protective devices.....Y
Schedule of items tested
basic protection by barrier or enclosure provided during erection.....Y
Insulation of non-conducting floors or walls......Y
Verification of voltage drop.......Y
Page 5 Circuit Details.
Supply to distribution board is from "Local Authority"
"overcurrent protective device for the DB is......"5419" (that is a switch and not an OCPD)
Type of wiring......CCCC
Reference method....AAAA
Circuit 3 Boiler.......Found that this circuit is connected to the switch for the removed immersion heater
Page6 Schedule of test results
R1+R2 for the cooker.......0.28 The cooker is very close to the DB so this is easily seen to be too much. This was tested by me to be 0.06 ie 6metres away.
Max Ze for lighting circuit .....N/A (when the R1+R2=0.64)
UNBELIEVABLE THis from a Fully qualified NICEIC registered Part P compliant IDIOT.:red cardheadbang
Page 1. Shows "unsatisfactory" yet on page 2 "satistactory" is shown.
Page2. One of the listed faults was " all circuits have 3871 typ2 MCBs in use" code 2
Also " No neutral continuity on the socket circuit" code 3, No RCD protection code 2, 240v fan above bath code 4.
Page3. The cert was only valid for 1 year yet (2 years ago) no'one has ordered a new cert to be issued
It was given 1 year "provided that any items given a code 2 must be remedied without delay. 2 years later and still no RCDs etc.
TNS ticked when it is TNCS
U1 230v Uo 240v
Ze 0.2 when it is 0.07
1361 Main fuse at a supposed 60A, yet he has put 100A as Max demand in a 1 bedroom flat with no shower.
Water and Gas bonds both ticked.
When i looked neither were connected and no evidence of ever being connected just stuffed in long lengths behind units and gas pipe boxing. (all kitchen and boiler work was done prior to the test.)
Means of earthing
Distributors facility ......N/A, Installation earth electrose........N/A
Page 4 (tick sheet)
Basic protection...obsticles Y...Barriers Y..placing out of reach Y
Fault protection
Prescence of earthing arrangements for combined protective and functional purposes ....y
Electrical separation
for MORE than one item of equipment...Y
Presence of diagrams...Y
Labelling of protective devices...Y (Even though an MCB is still labelled as immersion when it has been removed and replaced with a combi)
Presence of undervoltage protective devices.....Y
Schedule of items tested
basic protection by barrier or enclosure provided during erection.....Y
Insulation of non-conducting floors or walls......Y
Verification of voltage drop.......Y
Page 5 Circuit Details.
Supply to distribution board is from "Local Authority"
"overcurrent protective device for the DB is......"5419" (that is a switch and not an OCPD)
Type of wiring......CCCC
Reference method....AAAA
Circuit 3 Boiler.......Found that this circuit is connected to the switch for the removed immersion heater
Page6 Schedule of test results
R1+R2 for the cooker.......0.28 The cooker is very close to the DB so this is easily seen to be too much. This was tested by me to be 0.06 ie 6metres away.
Max Ze for lighting circuit .....N/A (when the R1+R2=0.64)
UNBELIEVABLE THis from a Fully qualified NICEIC registered Part P compliant IDIOT.:red cardheadbang