Two Live Wires One Neutral

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Harvey

Member
Joined
Oct 17, 2009
Messages
78
Reaction score
0
Location
Cambs
Came across CU in shed which is TT supplied by two 2.5 in parallel but one 2.5 neutral from another Db.So this is like a ring for the live wire .The supply cable is SWA buried The two 2.5 wires are on a 30A rewireable.What do you think ?   Satisfactory or not

 
If Im understaning this correctly you have the neutral supplied from on DB and the Line from another DB.  If this is correct then no it is dangerous especially for TT which requires both Line and neutral conductors to be disconnected for Isolation purposes from one double pole switch.

Also thinking about it further then if the cct was fully loaded then all of the current would be flowing down a single neutral conductor and you cant run undersized line conductors in parallel to share a load.

 
Last edited by a moderator:
Oh right quick before im off for tea, Line and neutral conductors need to be same csa so one of the line conductors needs to be disconnected and protective device suitably downrated taking into consideration design current and voltage drop. 

Need more info is this one or two armoured cabled? 

 
Okay, so you use 2 cores of the SWA one for L, one for N.

You size your OPCD for the cable CSA and it all works. (which I don't think it is in this case)

But the volt drop is marginal, right on the limits, and you notice the light in the shed dim a little when you switch the heater on.

So you connect the spare core in parallel with the L core to lower the volt drop a bit.

Nothing is being overloaded.

What's technically wrong with it?

Yes is might break a regulation or 2, but it's not dangerous is it?

 
Last edited by a moderator:
yes, a circuit that is designed for 30a, but the cable (neutral anyway), probably cant take that
No

I was saying size the OPCD for ONE cable, so say 16A.

Then the neutral can comfortably handle it, and the two parallel L's can handle double the current.  What's TECHNICALLY wrong with that?

In the OP's case, with a 30A OPCD it probably is wrong.

 
Last edited by a moderator:
No

I was saying size the OPCD for ONE cable, so say 16A.

Then the neutral can comfortably handle it, and the two parallel L's can handle double the current.  What's TECHNICALLY wrong with that?

In the OP's case, with a 30A OPCD it probably is wrong.
nothing wrong with doubling up on only line, provided OCPD is designed for the single conductor, but in the OP's case, it cant

 