Mastbruch
Downlights Tripped
Mastbruch
Just looking for a bit of help. Just finished fitting some Downlights and they have tripped the downstairs, the wiring all look spot on yet when I tried again only 3 of the 8 lights worked.  I have a tester should I test continuity from the switch or would an IR be appropriate.
Thanks.
Share this post
Link to post
Andy™
you should have already tested continuity & IR before it was energised. my guess is you failed to IR and not detected a fault, once powered up its tripped the breaker but blown fault apart which is why it now doesnt trip but only some work
id be looking for a fault at the last light that works or the first light that doesnt work
Share this post
Link to post
ProDave
Start by looking for the wiring fault at either the last of the 3 working ones, or the first of the remaining non working ones.
EDIT: Beaten to it by Andy
Edited by ProDave
Share this post
Link to post
Murdoch
Tripped mcb or rcd?
best you go to basics of dead testing
Edited by Murdoch
Share this post
Link to post
Mastbruch
Thank you
RCD Murdoch
Really peed off I didnt do the tests before hand Andy, very annoyed with myself.
Share this post
Link to post
Murdoch
17 minutes ago, Mastbruch said:
Thank you
RCD Murdoch
What do you mean peed off .... the bang test is NEVER recommended.
no sympathy
Share this post
Link to post
Tony S
Do you have the required test equipment? Your previously started threads would suggest you don’t.
Share this post
Link to post
Mastbruch
Yes Tony I have Kewtech MFT. I wouldnt of said I wished I would've tested them before if I didnt have a tester.
no sympathy
Agreed Fully
Share this post
Link to post
Ardet R
At least you have now had good experience of why the dead testing must be completed before powering up, and you will remember this in the future and it will ensure that you test correctly.  In this case there is no major damage so a good lesson learnt.
Share this post
Link to post
Mastbruch
Defiantly Ardet lesson learned mate.
Share this post
Link to post
Mastbruch
Just done an IR and that all went through smoothly. Got 2000 L/N 2000 L/E 2000 E/N Then I tested at individual Downlights and I am getting a reading from 0.23 from 4 of them then when pressing the switch 2000 which is fine but the other downlights just getting 2000 when pressing the switch on and off. It so much easier doing it at college yet completely different when you have to do it for real so to speak.
Share this post
Link to post
Andy™
the real world is completely different to a light & bit cable stuck surface in a little traning room
Share this post
Link to post
Mastbruch
Agreed.
Any ideas about above Andy?
Share this post
Link to post
Andy™
faulty mights maybe? did you zap the electronics at 500v instead of 250?
Share this post
Link to post
Mastbruch
No took all bulbs out and devices unplugged and passed the IR.
I really do enjoy fault finding just a pity I am not very good at it as I cant work out why I am only getting readings on 4 of the Downlights. Might have to look at the wiring within the Downlight.
Share this post
Link to post
Andy™
are they LED or halogen? if halogen then with the lamp removed you should be getting a very high IR reading between all 3 conductors. LED and you will get a very low, L-N and high L-E, N-E.
what points are you testing at?
Share this post
Link to post
Ardet R
You only have three lights that worked so after that third light there is a disconnection.  Because of the disconnection all readings after that in the circuit are high because there is no complete circuit.  Presumably the four lights that show a low reading were the three that had been working and the fourth is the location of the disconnection.
When testing at the downlights with the switch off all readings are high but with the switch ON the readings are low, this would indicate that the fault (between whichever conductors you are testing) is before the light switch, this is slightly odd because you had some working lights which were not tripping and often the fault would be near the disconnection.
However 0.23MΩ is not enough to trip an RCD so the fault may be only partial now.  I would therefore be checking the wiring in the switch to see if there is a damaged core almost touching the back box.
I would also look at light four and reterminate the connections.
Then re test IR to ensure the fault is clear and also at end of circuit do R1+R2 and compare with Rn + R2, they should be similar if the disconnection is cleared.  Remember on IR to test LE, NE, LN and compare readings.
Share this post
Link to post
Mastbruch
@Andy I tested at the CU for the IR where I tested LE, NE, LN and after this test I then linked the line & earth where I tested first at the socket between the SL/CPC then my R1 and R2 at the last light.
@Ardet because they are cheapy LAP Downlights from Screwfix the terminal box was so tight to get the wires in maybe a couple have came loose.
Going to check the terminations again when I get home.
Share this post
Link to post
Ardet R
Ok because i did not know you were doing R1R2 or what units you were giving results in I assumed it was still IR, however the results of the R1R2 show the low readings to be connected lights high ones not connected so still check light four connections, the fault sems to have cleared but check for cable damage or loose connections.
Share this post
Link to post
Mastbruch
All sorted now cheers for the replies
Share this post
Link to post
Andy™
so what was the problem?
Share this post
Link to post
Mastbruch
In the thread I said about buying cheap LAP Downlights from SF, We'll after closing inspection the neutrals which were already connected in the connector box's were not terminated properly & had a sleeve over them & it wasn't until I removed the sleeve and bingo.
Share this post
Link to post
Doc Hudson
But what was the cause of the tripping?
Share this post
Link to post
Andy™
i find it hard to believe that you have 5 out of 8 lights all with the same fault on neutrals not conencted correctly. and as above, a non connected neutral will not cause it to trip, it simply just wont light. so what did you really do?
Share this post
Link to post
Mastbruch
Just basically tightening everything back up and making sure terminations were right. Do you recommend another IR test
Share this post
Link to post
Create an account
Register a new account
Sign in
Sign In Now