spur for dishwasher

Question

red111

Good morning all.please see the picture attached , there is a cable coming from the ceiling ( one cable , and connected somehow to the main ring - i believe whether a junction box or else ) attached to a 13 amp fcu . the fcu outputs 2 cables

-one goes to a 3 pin socket to be used for a dishwasher ( the dishwasher is 10 amps itself ) --

and

-one  goes to a 3 amps  FCU   Then connects using a flex cable  to a boiler (boiler rated at  3 amps )

The switch board is old and does not have RCD .

 

is that enough or should i use RCD spur to replace the fcu or any where else .

any suggestions or help is really welcome. thank you .

 

advice rcd.png

Edited by red111

Share this post


Link to post
Share on other sites

10 answers to this question

Recommended Posts

  • 0
Andy™

you would be best replacing the consumer unit with a new one that includes RCD protection

Share this post


Link to post
Share on other sites
  • 0
red111
Just now, Andy™ said:

you would be best replacing the consumer unit with a new one that includes RCD protection

Thank you for the answer .  we just want a temporary solution until ready to change that unit . if safe off course .

 

Share this post


Link to post
Share on other sites
  • 0
Andy™

sticking in a single RCD to protect just 1 appliance isnt really going to be much of a benefit at all tbh

Share this post


Link to post
Share on other sites
  • 0
red111
15 minutes ago, Andy™ said:

sticking in a single RCD to protect just 1 appliance isnt really going to be much of a benefit at all tbh

leaving the current installation as it for now ( FCU outputting 2 cables ) is ok ?

Share this post


Link to post
Share on other sites
  • 0
Rob_the_rich
9 minutes ago, red111 said:

leaving the current installation as it for now ( FCU outputting 2 cables ) is ok ?

Depends on whether the cable coming down from the ceiling has anything else attached before it joins the ring, and whether it is surrounded by thermal insulation etc.

 

Note that an RCD fused spur to BS7288 is not in the list of RCD types recognised by reg 531.3.6 and therefore does not afford additional protection.

Share this post


Link to post
Share on other sites
  • 0
roys
4 hours ago, Rob_the_rich said:

 

Note that an RCD fused spur to BS7288 is not in the list of RCD types recognised by reg 531.3.6 and therefore does not afford additional protection.

 

Please excuse my ignorance, buts what is the reason that these RCD’s do not offer additional protection?

Share this post


Link to post
Share on other sites
  • 0
Rob_the_rich
29 minutes ago, roys said:

 

Please excuse my ignorance, buts what is the reason that these RCD’s do not offer additional protection?

You would have to ask JPEL/64 committee why they omitted bs7288 rcds (includes srcd socket outlets too) in the 18th. No BS EN numbers were quoted in previous editions as far as I can see. 

One guess is that you have both latching and non latching types in the same standard, which for socket outlet RCDs could introduce a danger on reconnection of supply with power tools etc or inconvenience eg fridges, but I don't know. 

Or perhaps they want to get away from individual appliance/point of use RCDs and prefer protection of whole circuits/groups of circuits, as in lighting and socket circuits.

Share this post


Link to post
Share on other sites
  • 0
roys

Thanks Rob, seems a strange one to me.

Share this post


Link to post
Share on other sites
  • 0
Evans Electric

Slowly but surely  this trade is strangling it's self  .   I was listening to a young sparky at the wholesalers  ... gave the impression he would be scared to open the toolbox everyday.   

Share this post


Link to post
Share on other sites
  • 0
red111

Thank you all for the advice

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×

Important Information

Terms of UseWe have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.