There is NO "maximum length"!what is the maximum lenght of cable you can have for socket outlets?
100 square metres of floor space, as posted above.ring equals=
50 or 75 square metres of floor space; as Theo already stated.radial equals=
Is it? Where do you get THAT gem of information from?????why is a ring preferred over a radial for sockets?
nuisance tripping could be heightened?Is it? Where do you get THAT gem of information from?????
By having radials instead of rings????????nuisance tripping could be heightened?
a 20a radial for socket outlets as oppossed to 32a ring willBy having radials instead of rings????????Explain please!
you could not have a 2.5mm protected by a 20a!ring 100m2radial in 2.5mm 50m2 20a
radial in 4mm 75m2 30a or 32a
thats floor area
17th page 363
did the heater scenario not hit the spot?^You seem to be suggesting that the 20 A radial will trip before a 32A ring?Define "trip"?
come to that..... define "well before"??? Well before what????
Sorry, but the post does not appear to make any sense. If you can explain yourself, we may be able to shed some light on the matter.
Why the frig not???????????????you could not have a 2.5mm protected by a 20a!
Why not? Could you explani a little.you could not have a 2.5mm protected by a 20a!
a 2.5mm will only carry 18amps so it could be overloadedWhy not? Could you explani a little.I was always lead to believe you could.
Theory my good man i am curious does it say anything in 17th edition regs about 4mm rings?ring 100m2
radial in 2.5mm 50m2 20a
radial in 4mm 75m2 30a or 32a
thats floor area
17th page 363
what fool would design a circuit if they new the typical load was going to exceed the fuse rating???a 20a radial for socket outlets as oppossed to 32a ring willtrip well before ! ?
a 20a radial would trip with just 2 3kw heaters plugged into it
but the ring would have amps to spare ! ?
Seems to missing his medication, too mate.what fool would design a circuit if they new the typical load was going to exceed the fuse rating???bit like saying....
And a 32A ring TRIP with 10.5kw shower wired in!!!
BUT a 50A RADIAL wouldn't???????
of no sensible use whatsoever?
You seem to be missing some very BASIC points of circuit design here bud...
i would like to think you don't need to get technically involved with a simplewhat fool would design a circuit if they new the typical load was going to exceed the fuse rating???bit like saying....
And a 32A ring TRIP with 10.5kw shower wired in!!!
BUT a 50A RADIAL wouldn't???????
of no sensible use whatsoever?
You seem to be missing some very BASIC points of circuit design here bud...